Greetings.

I want to get a cable from the fuse board up to the loft and think the best way is up inside the cavity of the wall.
I was wondering if anyone has any handy tips for doing this.

I intend to drill two holes in the wall, one at the fuseboard and one up in the loft but the biggest problem I can see
is fishing a cable up or down IE dropping a cable from the top and finding the hole in the bottom.
I think I might lose the fishing rod or cable in the wall and not be able to find it to pull it out.

So does anyone have any handy tips for fishing a cable up or down through a cavity wall?
Any comments appreciated.

Thanks.
 
As mentioned previously.............what happens when they decide to get cavity wall insulation?
 
Well the ideal thing to do would be to drop some sort of flexible conduit down the cavity to protect the cables.
Place the cables inside the conduit.

The other alternative is to take the cable or cables up the outside of the house in conduit.
The fuseboard is placed on an outside wall so I could drill straight through and run the cable up the outside of the house and then drill through and run the cable into the loft but this won't look very nice.

All the rooms in the house are occupied by tenants so lifting floorboard etc to get a good cable run is out of the question.

Does cavity wall insulation have a detrimental effect on cable insulation?
Does it break down the plastic in the insulation of the cable or is the only issue with insulation going to be correction factors for a cable placed in thermal insulation?
 
wazz it up the outside in black pvc conduit.
 
Does cavity wall insulation have a detrimental effect on cable insulation?
Does it break down the plastic in the insulation of the cable or is the only issue with insulation going to be correction factors for a cable placed in thermal insulation?

It has a huge effect on the current carrying capacity of the cable.

Up to half the rated current if run completely surrounded by insulation over 500mm
 
I wouldn't be running cables in cavity walls! Give it a year or two and you'll start getting damp patches on the interior walls where the moisture condenses and runs down the cable, seeping through the brickwork at points where the cable is resting on the other side of the skin.

Also, how do you intend to support the cable correctly throughout its run?
 
Yes cable support would be a problem.

The thing is I have seen or heard of this being done loads of times, cables in cavity walls I mean.
I thought it was common practice.
 
I have heard this done many times wiring in the cavities but only really in houses and never a cavity between to houses
 
Yes cable support would be a problem.

The thing is I have seen or heard of this being done loads of times, cables in cavity walls I mean.
I thought it was common practice.

It was common practice. In the 70s and early 80s when council houses and cheap housing association properties were being put up left right and center, nearly all of them had the typical skeleton unit arrangenent with all cables being whisked up the cavity to the floor above! Its cheap, shoddy and dangerous in my opinion. I've levered out a fair few flooded skeleton units in my time.
 