Yeah I have some they are rated at 40 amp, expensive though, better to use a through crimp if your a tight --- like me haha
I know what your saying, me too tbh, they are capable of coping with a 2.5 to a 6mm2 conductor and are 40 amp rated, I have some but haven't used any yet, I would generally through crimp to extend a cable if there was no other way, a 6mm2 cable anyhow, but they must have been tested for wago to sell them here under a BS number?
The standard wago box will take 6mm T&E cables but you will need to remove the cable clamp bars beforehand.
For 6mm cables you must use Wago 773-173 connectors, which are terminal current rated to 32amps. The wago box with this type of connector would then satisfy the Maintainance Free (MF BS5733) requirement.
As for jointing 10mm cables, I would only consider quality crimps with 2 pieces of heat shrink around each joint and then generously over-wrapped with self amalgamating tape.
Guys, you are all missing the fact that most push-connectors are only classed as MF once de-rated. Look on the Wago website to see how much by.
what about these? 1 million plumbers can't be wrong.
na..too big tel...
- - - Updated - - -
and i hate this jointing cables under floors stuff as well...
I had to repair a 10mm T&E shower cable recently, it had been ragged through a hole in the joist and the sheath and neutral insulation had been shaved off. Couldn't replace the whole cable, as it was routed through newly plastered and decorated house. I just routed it up to loft so it would be accessible and used a 60amp JB then used a new length for the last bit of the run to the shower isolator. Circuit ended up a couple of meters longer than it was before. This solution fitted the circumstances though. If I had no choice but to join under floorboards then I'd just crimp it!
What would be the advantage of two lots of heat shrink covered in SA tape instead of front to front insulation tape and then SA tape?
The 2 pieces of shrink is just me been picky. I just feel it gives that extra protection against anything piecing though. It's not such a risk with the insulated crimps because they already have that hard shell of plastic around the joint to protect it.
My question was more because I wondered why people favoured heat shrink over insulation tape. When I insulate bare crimps I usually backwrap the crimp with insulation tape to keep the glue out of the connection, then I wrap as normal, then I cover with a generous wrapping of SA tape.
I'm wondering what the advantage is of using heat shrink? To me it's a PITA!
Don't understand what's a PITA when it's at home??
Heat shrinked butt crimps look a far better installation than rolls of insulating tape round them. First layer of heat-shrink goes over the actual butt crimp, second layer goes over the overall connection onto the connected cable insulation. As all heat-shrink tubing is XLPE, it gives the crimped connection a better insulation value than the cables standard PVC insulation. Or where XLPE cables are crimp connected, maintains that cables insulation value...