Got to replace a CU and move it off the ground in a shop, would it be acceptable to mount the CU on the wall in the void between the ceiling and suspended ceiling
The only problem I can see are the meter tail being borderline 3 metres.

Thanks.
 
Sorry, maybe i got it wrong but are you saying that you trying to loose a fusebox above the ceiling?
 
It would be as it's a case of moving a ceiling tile to get to the CU, no tools required only a ladder

Hum, me think you need to say no to the client. Sure move it off the ground, but not to above the false ceiling. Tell them to loose a couple of shelves.
 
How do you do that thing of copying section of OP in a nice quote box??

Anyway.... Somehow, needing to get a ladder to access CU doesn't strike me as being particulary accessible.

Mount at height where someone can reach quickly in case of need.
 
How do you do that thing of copying section of OP in a nice quote box??

Anyway.... Somehow, needing to get a ladder to access CU doesn't strike me as being particulary accessible.

Mount at height where someone can reach quickly in case of need.

click on reply with quote Tony at the bottom right of the post and ensure you writing is below the last quote shown
 
Thanks chaps, might be a case of cutting a inspection hatch in the back of a shelving unit as CU is not easily accessible where it's presently situated
 