Still learning about my new job (streetlighting) and went out on maintenance yesterday. Lamp not working, so replaced it but its still wouldn't light up, doesn't even try (55watt SOX). Ballast putting out 230 volts. I phoned the office and they said they're supposed to put out around 500v to begin with.

Is that right, and if so, what causes them to only put out 230v?

Cheers.
 
im not familiar with the ballast as you haven't told us what the brand and model number it is
but most of them usually have a schematic on them.
or else you could look it up on the manufactures website.
 
Top tip for you mate. If the fuse is blowing its usually faulty ballast / capacitor / cell. Fuse intact usually faulty lamp / ignitor / cell. I'll bet you its a faulty ignitor.
 
ignitor 97% of the time
new lamp faulty 1%
lamp holder centre contact corroded 1%
ballast 1%
 
Fuse ok, definitely the ballast, I chucked another one in and it fired up. I'll try and get a picture.
 
Top tip for you mate. If the fuse is blowing its usually faulty ballast / capacitor / cell. Fuse intact usually faulty lamp / ignitor / cell. I'll bet you its a faulty ignitor.

Cheers, i don't carry spare ignitors, they're part of the fitting, but separate ballast and capacitor fitted in column base.
 
Must be old install. Some old Sox lamp use to have ballast and ignitor intergrated into same housing/ballast and installed at bottom of colum as you have described. Very rare these days!
 
I was just interested to know if anyone knew what actually causes the ballast to fail.
 
I was just interested to know if anyone knew what actually causes the ballast to fail.

breakdown of core insulation , usually overheats and melts , and nearly always takes out the fuse.

Must be old install. Some old Sox lamp use to have ballast and ignitor intergrated into same housing/ballast and installed at bottom of colum as you have described. Very rare these days!

nope , still millions of "remote gear" street lighting around the UK , nearly always sox.

Still learning about my new job (streetlighting)

yet started arguing the ---- over a recent feeder pillar rewire thread , oh the irony lol.
;-)
 
Not been on street lighting for a fair few years, but can remember an old spark telling me the local scrap yard paid £1 for each old ballast, surprising the amount he used to have go on him!!!
 
breakdown of core insulation , usually overheats and melts , and nearly always takes out the fuse.



nope , still millions of "remote gear" street lighting around the UK , nearly always sox.



yet started arguing the ---- over a recent feeder pillar rewire thread , oh the irony lol.
;-)

arguing about what?

No overheating evident, Fuse intact.

Biff, this is all new to me, and I have no problem asking for help from more knowledgeable people. Do these ballasts put out 500v on start up, then go down to 230v? I would like to know HOW these things work, and apart from coming on here and asking my 'friends' what do I do? Sure, I can go around blindly replacing components, but all I will be is a fitter.

Believe me, by hook or by crook, I WILL find out, and then i will share what I have learned.

You can be part of the process at the start, or the end.

x
 
THIS is the end, my only friend, the END.

No seriously, I've pulled your leg in a few recent threads biff, but I would like to understand the science behind the systems I'm currently working on. If you can help, I would greatly appreciate it. By all means, pull my leg a bit ( I played Devils' Advocate over the MET thing), but I've been here long enough to deserve a bit of respect, and I'm honest enough to ask for a bit of help.

xx
 
and why are you blowing kisses at me ?
flattering im sure but highly inappropriate , unless youre trying to wind me up.
:-)
 

OFFICIAL SPONSORS

Back
Top