  1. jaydee81

    Self Employment

    i for one am going the other way have recently gone back to being employed and just do little jobs evenings and weekends and am far better off financially
  2. jaydee81

    Earthing on a domestic TT supply system with submain, advice needed please

    earth rod should be at the origin of the supply so install new rod and connect it to switch fuse, then connect both rods together will give you a better overall Ra
  3. jaydee81

    heating connections

    would need to control ufh pump through a relay honeywell u plan shows set up
  4. jaydee81

    heating connections

    would suggest looking at the honeywell wiring guide issue 16 the s plan plus shows 3 zone valves one hot water and two heating zones would just need to incorporate a couple more connectors in wiring centre
  5. jaydee81

    Too large a ring main

    i know but why cant it be changed to a b type
  6. jaydee81

    Too large a ring main

    am i missing something from the original post the measured zs was 1 ohm max zs for b 32 is 1.15 ohms ?
  7. jaydee81

    Too large a ring main

    whats the circuit supplying could you not fit b 32
  8. jaydee81

    Too large a ring main

    whats the reason for it being on a c type mcb?
  9. jaydee81

    Too large a ring main

    maximum floor area for a ring is 100m2 tho can see why its not been put on a rcd with that amount of I T equipment on it
  10. jaydee81

    Too large a ring main

    just out of interest what was your ze
  11. jaydee81

    Caravan park

    your rcd at the hook up point is the easiest one to test, disconnect caravan and test at rcd terminals the caravan rcd not so easy only way to test it would be too temporary link out or replace hook up rcd with main switch and replace after test
  12. jaydee81

    Newbie looking for answers

    hello and welcome hope we can help
  13. jaydee81

    Drayton 3 port valve - confirmation of fault?

    Are u sure it's wired correctly as heating on should be white hot water off is grey and hot water on is orange
  14. jaydee81

    help with central heating s plan plus newbie

    check out honeywell u plan wiring diagram all will become clear [honeywell wiring guide issue 16 pdf]
  15. jaydee81

    help with central heating s plan plus newbie

    yes a 16 amp dedicated supply to immersion heater element and cylinder stat wiring not sure on your set up but guess there is a pump for heating and hot water and a separate under floor heating pump its the under floor heating pump that needs a relay because the zone valve needs to be open...
  16. jaydee81

    help with central heating s plan plus newbie

    your mega flow cylinder will have a immersion heater element and a cylinder stat basically hot water on from programmer to common on cylinder stat normally open contact to brown of the valve as for your underfloor heating there is normally a wiring centre supplied with the kit which does all the...
  17. jaydee81

    Garage supply. RCBO at CU? RCCB at garage board as well

    Would run swa to feed garage rcd cu from a mcb in main cu dependent on earthing system of course
  18. jaydee81

    S plan system with 2x under floor heating zones

    Would use individual programmable stats for underfloor gives customer move control
  19. jaydee81

    no earth wire from meter box

    be prepared to install new rod or two
  20. jaydee81

    no earth wire from meter box

    definately would be gaining access to check if there actual is an earth rod my reckoning is that the water main is being used as an earth