I recently tested a new build (mostly new build) and found 45 sockets on a large ring main in an office environment.
My r1 was 1.6 ohms rn 1.6 ohms and r2 was 2.7 ohms which made my r1+r2 1 ohm roughly
my zs on the circuit was also 1 ohm although I didn't test all of them.
the protective device is a c32 MCB, common sense tells me this is wrong but can anyone tell me why and how to explain it to a spark who has done this twice aslong as me.
No Rcd needed as it's a managed building and all surface work although I would of used a RCBO
 
Forget 'roughly', you need to deal with 'exactly'.

So - what, exactly, was your measured Zs on the circuit? And, what does the BGB say the maximum Zs for a C32 needs to be?
 
I can foresee many potential issues with this circuit, btw, but let's start with what we know......
 
The feed to the DB is 25mm 4 core. Armour used as earth
zs of this board is 0.2
what is BGB. I know I need to be exact but sometimes I not sure to trust my meter even know it's was new this year
 
all depends on the loading of the circuit. worst can happen is the MCB will trip. bad design though. although i don't know of a reg. stipulating max. no. of sockets on a RFC, i consider any more than 15 is too many. should have been 3 circuits, IMO.
 
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm
 
Thanks for all the great answers
i originally told them 3 ring mains was the answer but when they questioned me I couldn't really back myself up.
Would a RCBO solve the problem as the max zs would then become 1666
 
Problem is, in office environment, total leakage might be too high either for single RCD/RCBO or for a circuit without high integrity CPC. Even if you can get the breaker to stay in, it's bad design.
 
no. that's the cowboy solution. you might just get away with 2 radials on B20 or B16 MCBs.
 
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm

Indeed, if you split it in the middle, your (R1+R2) will double. If split asymmetrically, one radial will be better than that, and one worse.
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly
 
An alternative way to reduce the Zs might be to provide some additional path(s) to earth (i.e. supplementary bonding), if the installation lends itself to that?
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly

In 2.5mm T&E with 1.5mm CPC, then r2 (for CPC, not neutral) is approx. 1.67x r1.
 
Also not getting why no rcd protection on this large skt circuit if installation is maintaind by skilled and instructed Person . Wot about all the office staff surely not all are skilled and or instructed ?? In my opinion all SO unless labelled as so for a specific purpose ie IT hub . Potentially in youse of normal folk need rcd/rcbo
 
well if its an office with accessable ceiling voids and surface wiring it cant be that much work to pull in 2 extra legs to create 2 smaller ring mains ?
 
Also not getting why no rcd protection on this large skt circuit if installation is maintaind by skilled and instructed Person . Wot about all the office staff surely not all are skilled and or instructed ?? In my opinion all SO unless labelled as so for a specific purpose ie IT hub . Potentially in youse of normal folk need rcd/rcbo

im guessing you dont do much commercial design then ? :-/
 
You guessed Well. No not an expert , il be having a little reminder session in van tomorrow, if memory serves SO's <20a for youse of normal people need rcd protection . I know my max earth loops though and this one is over
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Too large a ring main
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--

Advert

Thread statistics

Created
Boaky,
Last reply from
Aindowsimon,
Replies
34
Views
4,724

Advert

Back
Top