For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm
 
Thanks for all the great answers
i originally told them 3 ring mains was the answer but when they questioned me I couldn't really back myself up.
Would a RCBO solve the problem as the max zs would then become 1666
 
Problem is, in office environment, total leakage might be too high either for single RCD/RCBO or for a circuit without high integrity CPC. Even if you can get the breaker to stay in, it's bad design.
 
no. that's the cowboy solution. you might just get away with 2 radials on B20 or B16 MCBs.
 
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm

Indeed, if you split it in the middle, your (R1+R2) will double. If split asymmetrically, one radial will be better than that, and one worse.
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly
 
An alternative way to reduce the Zs might be to provide some additional path(s) to earth (i.e. supplementary bonding), if the installation lends itself to that?
 
am i missing something from the original post the measured zs was 1 ohm max zs for b 32 is 1.15 ohms ?
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly

In 2.5mm T&E with 1.5mm CPC, then r2 (for CPC, not neutral) is approx. 1.67x r1.
 

OFFICIAL SPONSORS

Back
Top