Don't forget to apply 80% value if out of the reqs
Split the circuit turn it into 2 radials and change breakers to 20amp...
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).
I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm
am i missing something from the original post the measured zs was 1 ohm max zs for b 32 is 1.15 ohms ?
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly