Hi all new on here and looking for advice. I ran wiring for an extension and took a 13a spur from the ring main using 2.5mm2 t&e for the underfloor heating controller. The homeowner has got someone in to lay the the heating mat kit 20sqm of it and when the tiler connected to thermostat he said 1...
manny.p
Thread
cablecablesize
heating
main
problem
ring
ring main
size
spur
thermostat
underfloor
underfloor heating
i am struggling to work out the cable size required for the following air con unit. the run of the 4 core swa cable will be about 90 metres, where 85% of it will be underground.
I have to put in a 20A supply for a cabinet in a Spar shop.
I have used the voltage drop calculator and it has come out at 2.5mm t & e. It's only a 18m run ................ Some people use 4mm t & e out of habit for such an installation. Why? The old belt and braces routine!
Anyone got any...
Hi,
I need to replace a cable that is used at a scaffold yard to test the hoists. They currently have a 6mm cable installed but they say that when they try to test their biggest hoists the cable doesn't have the capacity and the hoists wont function properly. The information i have about the...
hello, can anyone help me , got to run a cable from a 11kv transformer to a 400amp main distribution unit which is 125m away, how do i calculate what size cable is required and is there a site where i can put in all the details in and it calculates this for me, thank you
A customer has bought a Rangemaster cooker 14.8kw, Rangemaster state the FLC is 55amps, cable wiring ref method is 100.............what cable breaker size should I use. This is for a domestic property?
Hi,
I'm installing a 10.8 kw shower and looking at other forums everyone is saying 10mm is OK however i can't see how.
10800W/230V=47A
breaker size 50A
the only way it can be a 10mm is if its clipped direct with no insulation as it can take 64A however if it is any other reference then the...
Good afternonn,
I am new member in this forum and it's my first participation that I hope will not be the last!
I'm a mechanical ingeenier and I'm looking for the complete and correct manner or formula to determine and calculate a cable section in a three phase circuit.
It will be very helpful...
Hi Can anyone remember which came first, the change of cable size to metric from imperial or the change to brown for live conductor? I've come across a cooker supply cable with new colour code of Brown,Blue + Earth but it is 7 stranded. Difficult to tell it it is 7/029 or 7/036. Could be the...
Hi Got situation with one of these heaters. pretty juicy. It does heating & Water. 3-9kw
http://accl.onwirral.net/Downloads/Heatrae_Amptec_Installation_Guide.pdf
Its going to be wired Y Plan but issue is that its being asked of me to put 10mm cable in. Which i would agree on is suitable
BUT...
Lads when ive earthed an array TL invertas ive always used 10mm G/Y to earth rod! another company i have fitted one for had inspection and were told it should be 16mm ?? thats b----ks is it not?
Hi All
Got a 3 phase 20A per phase supply coming in, feeding 2 gites. The owner needs the 3 phase supply to also feed a new house 66 meters away. The house will only single phase loads and probably be unbalanced most of the time
Now the tables I have, show that for a single phase - the wire...
fjr1300
Thread
3 phase
cablecablesize
loads
phase
roman
single
single phase
size
supply
times
Hi there, I hope you can shed some light on this for me. I have an installation with two 32A frc's both in t&e what I measure at 2.5/1.5. Measured end to end resistance on L N and cpc, in both circuits the cpc is showing double the value of the L and N conductors to within .o5 ohms. I have tried...
Hey all. Hope everyone is well.
Ok, I'm currently doing a rewire on a ground floor flat. The entire job will be done in trunking and I have an apprentice with me. Now, my intention is to run a 10mm cable to the shower as it's 9.5kw (I do this as a rule of thumb).
This is also in our company...
Hi just about to have a oven 3.6kw,combi microwave 3.6kw,hob 6.6kw fitted,the electrician is splitting the original 6mm cable to seperate isolation points for these appliances,my doubt is ,is this cable big enough electrician assures me if the diversty is taken into consideration the cable is...
Hi Guys,
In our place we have several machines that are fed from 63A sockets. The supply cable to the machines is CY and currently
6mm has been used which is no good for 63A
But the 63A sockets are fed by a 32A breaker.
Is it ok to use the 6mm as the socket is fed by a lower rated breaker...
dasrik
Thread
attach
cablecablesize
canada
correct
found
machine
ratings
size
socket
supply
hi i am doing a job for father in law 10 outside brick lights using low energy lamps and 4 double s/o the lenght of the run is 60 m could i get away with using 2.5mm if i put it on 10 a breaker the s/o are only for light use like radio the lights will be on a fcu thanks
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc