tncs

  1. J

    TN-S / TN-CS PME?

    Hi, Just reading this National Grid Sticker and it said the earthing is TN-S derived from a PME, I thought PME was only associated with TN-CS systems? Thanks, James.
  2. P

    TNS or TNCS ?

    As per the title, what type of earthing system is this ? From the sheath of the main incoming cable, underneath the main cut out, is a cable going to the MET block, looks original/very old, from this MET block come various earths going off to consumer units and switch fuses etc, so, TNS. However...
  3. G

    TNCS upgrade to 16mm earthing conductot

    Hi all. Is it my responsibility or the suppliers responsibility to upgrade the earthing conductor on a TNCS system from 10mm to 16mm. I'm completing a CU upgrade for an Elecsa assessment and as part of this am replacing the Meter tails and the earthing conductor to comply with current...
  4. B

    Connected as both tns and tncs

    Done a board change yesterday and was renewing the meter tails when i noticed that the incomings sheath was bonded like on a tns system but there was also a 4mm earth link from the neutral side of the fuse carrier to the earth henley block which would normally mean tncs. i upgraded this 4mm to a...
  5. M

    Caravan tt tncs

    Hi There is a caravan that moves between two properties. One property is Tncs supply the other tt. Both feed caravan via external socket on property which are 16amp radial (rcd protected ) . Caravan plugs into this via 25 meter lead. Caravan has small cu with 30 amp rcd,, 16amp mcb, 6 amp...
  6. T

    Tncs supply, can i take the earth outside the buildinh?

    Hi planning to wire a new build house supplied by tncs. The meter and isolator have been installed in the garage which is seperate from the house. During my college days i was always told not to takethe earth outside the building. Iv never come across the mains being in the garage so unsure...
  7. S

    DIY TNCS - Advise Needed

    Started a job today running in cables, after the customer cleared out the coats and shoes from the meter cupboard I find this DIY bad boy. A clamp on the outer containment of the incoming main - I did a quick loop test on the socket with reading of 0.40ohms. Will do a full ZS and ZE when I go...
  8. E

    Caravan and tncs

    The other day I had to connect a static caravan so the house holders can live in it while their house is being refurbed, the house is tncs no I know your not ment to export the earth and I understand why, so I installed a earth rod, 78 ohms. the main board in the caravan has 30ma rcd, but I...
  9. M

    Tncs m.e.t

    Hi all Went to look at a consumer unit change today. Supply is tncs all bonding is correct. I noticed that where the supply is there is no main earthing terminal. The consumer unit has been used for all bonding and circuit cpcs. Just wondered weather i should install new met at point of...
  10. S

    TNCS Outbuilding earthing arrangement

    I have a large shed (affectionately known as the warehouse) that is fed by a 16amp rcbo. The main earthing arrangement at the distribution boards is tncs and now a more experienced electrician than myself has stated that the earth in the 3 core 2.5mm armoured cable should be connected to a...
  11. L

    Ze TNCS too high

    Hi, my father inlaw had the Scottish Power in on Friday to install anew supply to his new build, then the meter bloke came later in the afternoon. Went there today so I could get his 19 way DB installed and the place tested so I can have some peace tomorrow and Tuesday. When I came to test the...
  12. N

    Earthing system , TNCS off a TNS?

    It is possible to have both TN-S and TN-C-S supplies from the same transformer. For example, the sheaths on some underground cables corrode and stop providing good earth connections, and so homes where "bad earths" are found get converted to TN-C-S
  13. P

    Is this a TNCS PNB? Large Commercial Site with local 11KV Tx

    Hi All Sorry for the poor photo's, just after some clarification as to the arrangements at source of the supply below. No info from the DNO with little info available in the sub. Photo 2 clearly show a PEN between the neutral and the earthing bar in the section board. I am presuming this to be...
  14. I

    do you still need to contact DNO when exporting TNCS earth

    hi dont want to open the usual debate re tncs earth, looking for where i can find out the answer as to weather the DNO still needs to give permission for there earth to be exported any one help ?
  15. R

    Using SWA Armour & Core in PME TNCS?

    Hi guys , was wondering if any could advise. Got a job when client is moving his shed containing Swin pool pump filter etc etc a few metres. I have disconnected for him and made safe. Unfortunately though he thought he could just bish bosh in himself but advised that would be a notifiable and...
  16. D

    TT Suply to a TNCS

    I am wiring a garage and bedroom extension to an Ex council house in a small local village, the supply is a TT, I have been told that the suppliers will change it to a TNCs supply. I would much rather the TNCS. I would have to install a new earth spike as the origional is under the concrete...
  17. S

    TNS or TNCS - which is preferable?

    Hi there, I'm the proud owner of a Victorian, 2-bed semi and recently discovered that my only means of earthing look to be my water supply and (redundant, non-conducting) gas pipe. I managed to get UKPN to come out and do a PME availability check, having been told all sorts of things by them...
  18. U

    southern electric tt to tncs

    Hi all, I was at a job with a tt system and a ze of 299 ohms, so made a call to see if it was possible to swap to tncs. Normally I call western power they tell me if they think its possible,send someone out, if it is possible they put the connector in, put a sticker on and send me a bill. now...
  19. F

    Size of earth on tncs system

    Am i right in saying that you had a 10mm earth wire from the service head to the consumer unit on a tncs supply, measure the ze, and use this value to work out your fault current, and put it into the adiabatic equation, then if the value was ok, leave the 10mm in place, instead of replacing it...
  20. R

    Lack of trust in tncs

    Hi guys, In the past week have been to 3 call outs where customers are getting shocks of exposed extraneous and conductive parts. Both because of loss of neutral in the supply. Well CNE conductor. I think this is ridiculous. And the suppliers don't seem to be aware how dangerous this is...