tt earth

  1. S

    Equipotential lead direct to a TT earth stake

    Had a interesting scenario crop up this week when was asked if it was ok to take a new 10mm equipotential wire from gas pipe to outside earth stake onto a new earth clamp below the existing 16mm earth conductor clamp rather than go all the way back to the MET. If not ok can someone suggest a...
  2. La Poste

    TT Earth and Neutral voltage.

    Just out of interest if a TT system is installed with a decent earth rod what sort of voltages exist between the Neutral in respect to real earth potential of 0 Volts? What's the average Neutral to Earth voltage, does it fluctuate from time to time? Does it get dangerous??? Thanks.
  3. D

    TT earth system?!

    Hello fellow sparkies Been asked to change a CU in an old persons home, he said it had a re-wire 20 years ago but the earthing method I have not come across before. The main earth is on a lead water pipe coming from ground, this goes to the main terminal on DBoard and then equipotential...
  4. keniff

    tt earth rod.

    hi guys i dont do alot of work on tt setups in my area, just done a few bits, new ring and lighting circuit for an extension, do i need to include earth rod resistance on my eic? thanks in advance
  5. R

    TT earth problems

    Hi all, just heard about this forum and decided to give it a go. :) I've only been a sparky for just over 2 years and last week a mate of mine who's a general handyman fitted a 12v door bell for a lady which is mains fed to a transformer. He wired it into a JB on the lighting circuit in the...
  6. U

    tt earth problem

    is it possible to install an earth stake inside a building {underfloor} rather than outside as house surrounded by concrete or is it better to go through concrete leaving stake outside
  7. D

    Broken TT earth cable

    Can I have some thoughts on a broken TT Earth. The house owner has cut through there TT Earth cable 3 feet up from the stake. Can this be jointed and if so what would be a suitable connection, in an ideal world a new continuse cable would be preffered or is this the only option. I could not...
  8. K

    TT Earth Loop Impedence

    Hi Just joined the forum today and I have my NIC inspection tomorrow. Wanted to check whether they will fail me as the Impedence is 3.74ohms which is over the limit and also means my RCD trips at 33.4s on 1x. I am aware that this is high and will put another rod in which means upping the floor...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock