Hello fellow sparkies

Been asked to change a CU in an old persons home, he said it had a re-wire 20 years ago but the earthing method I have not come across before.

The main earth is on a lead water pipe coming from ground, this goes to the main terminal on DBoard and then equipotential bonding and also the linked circuit bonding run off there.

My question is, when running earth tests do I do the same tests as it were a TT system? Or should I install an Earth rod to be on the safe side? I did a quick ZE check just of incoming and was only 8.54 ohms, this was with all earths disconnected, except the one going to earth.

Just wondering if you older...er i mean more experienced chaps on here who have come across this know about it.

The house is an old cottage and neighboring proterties are on rods

Thanks for you time in advance.

Dan

;)
 
Last edited by a moderator:
The use of public service supply pipes as installation earth electrodes is not permitted, 542.2.4.

You will need to install an installation earth electrode and an MET for the installation.
 
used to be common to use lead water pipe for earthing. not now, as new mains are put in they are in plastic. your options are .1. Put an earth rod in . you need the Ze to be<200ohms. , but everything in the property MUST be on RCD to meet disconnectin times. 2. Contact DNO ( supplier ) and ask them if they will PME it.
 
Thanks for the quick responses chaps. All really helpfull and I wanted to put the ROD in as the owner didnt want the cost of going PME.

Thanks again chaps :)
 
in the old days the lead water pipes ran for miles and got bigger and bigger, in short an excellent earth
older properties used to have 2 wire circuits to immersions and the like, using the water pipe as the earth
but not now its probably been changed to PVC outside or will do soon
plus you will need to bond the incoming water pipe and the gas if fitted
20 years ago we did not use water pipes as an earth on TT systems people tell you any old rubbish to save money
I had one tried it one with his old lead sheathed cables!!!!
 
I will try and stir this thread up a bit by asking you for an interpretation of 542.2.4

My interpretation is that an obsolete water pipe may very well be used as an electrode, if the pipe is on your property,unused and unlikely to be removed by others
Your veiws ?
 
No don`t use the old lead pipe because some tatter will steal it, or in afew year they will put a bigger drive in and remove it with the digger and then some clever sod will sue you. Always cover your back. Put the rod in the ground if it meets all the ticks all is well and you have done a good job.
 
mm seem to recall that subject, but i was told that only if the water pipe was on land owned by you
a farm would be suitable , but as the other chap says the robbing toe rags would be round
I have just had to run the bonding to the gas and water pipes outside a listed property (not allowed inside) however i ran them in pvc conduit and then it ws painted over to match, it was a pig to do but the roaming copper thieves will not see it so easilly
locally we have had a great many earth cables removed from agricultural buildings and the like, even supply cables between buildings

it does go wrong for them now and then But I cannot make a statement on a public forum as I dont want to help them!
 
I will try and stir this thread up a bit by asking you for an interpretation of 542.2.4

My interpretation is that an obsolete water pipe may very well be used as an electrode, if the pipe is on your property,unused and unlikely to be removed by others
Your veiws ?

If it is a private water supply i.e you own it and it is on your land and there is no chance of it being dug up and/or replaced by anyone except yourself then you are permitted to use this pipewrok as an earth electrode.

Like I said in my previous post though, if it is a public, utility company supply pipe then absolutely not.
 

Reply to TT earth system?! in the Australia area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
574
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
791
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock