vxwestie

I need to install ct metering to a submain and it requires a 10amp three phase mcb. I actually need to do this in two different locations for two different jobs.
think I'm having brain fade, but any ideas how I can mount this mcb off a 400amp busbar chamber without installing a complete three phase disboard.
seems stupid to install a complete board for one mcb especially when the smallest board is 4way... I don't have a huge space either, a 4way board would be tight...
 
image.jpg

This is what I'm proposing to re-arrange.
 

Attachments

  • image.jpg
    image.jpg
    117.5 KB · Views: 76
Bung the mcb inside an enclosure.
 

Attachments

  • image.jpg
    image.jpg
    12.5 KB · Views: 9
  • image.jpg
    image.jpg
    11.5 KB · Views: 10
Whoever did that job originally needs stringing up! How on earth could they have ever been let loose on the tools in the first place?!?!?
 
Whoever did that job originally needs stringing up! How on earth could they have ever been let loose on the tools in the first place?!?!?

Phage to agree with you there... It's a major job to put right as all the cables are very short, but they're only 185mm !!!

thats only the half of it... No isolation devices, no barriers, etc, etc...
 
  • Like
Reactions: 1 person
Being really dumb now, but will just the mcb in an enc be ok? Must read through the regs, can overload devices be used as service isolators, or should there be a main switch be in circuit?


...... Reaches for regs book....
 
Depending on the bus bar system you can get "plug in" enclosures which you can mount a MCB in.
We have them feeding ovens.
 
In fairness, the 25mm tails off the busbar are just supplying ct metering at 10amp and a dual socket.
the 185's are carrying 460amp

my issues amongst many are the mcbs in an unprotected busbar chamber
 
In fairness, the 25mm tails off the busbar are just supplying ct metering at 10amp and a dual socket.
the 185's are carrying 460amp

my issues amongst many are the mcbs in an unprotected busbar chamber

No different to thousand of industrial cabinets throughout the land then...
 
In fairness, the 25mm tails off the busbar are just supplying ct metering at 10amp and a dual socket.
the 185's are carrying 460 amp

my issues amongst many are the mcbs in an unprotected busbar chamber

Those busbars don't look anywhere near suitable for 460A, look more like 200A rated bars!!!

Agree with Mr D, that busbar panel looks like a complete pig's ear of a job, as does the other panel too!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
1 way 3phase board
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
vxwestie,
Last reply from
Engineer54,
Replies
10
Views
109

Advert