What ? 16mm isn't good enough? 63amp 30ma RCBO protection... Is that not how you would do it?
 
Method... In walls and floor board , would need to check regs for Letter. I prob will get a m8 for core drilling and chasing , the supply is three phase.. Are you saying that's not enough?
 
Why do you think you need 63A for a bedsit room?

How are the bedsits to be metered?

If you attempt this job on your own you will never keep up with other trades - you need to reconsider this.
 
Why do you think you need 63A for a bedsit room?

How are the bedsits to be metered?

If you attempt this job on your own you will never keep up with other trades - you need to reconsider this.


I am supplying each room with its own board so rooms can be upgraded in the future. I.e to include a electric shower . But also clamp meters may go on in the future if elec bill are tooo high. I agree I will need to work hard n fast to keep up but I'm game .. If it gets on top I'll bring someone in.
 
How is the installation going to comply with BS7671 if each flat is only covered by one 30ma RCBO?
 
How is the installation going to comply with BS7671 if each flat is only covered by one 30ma RCBO?

Shushhh!! lol!!

More to the point, how is he going to overcome discrimination between RCD devices at the origin and any RCD devices in the bedsit's??
 
Last edited by a moderator:
How is the installation going to comply with BS7671 if each flat is only covered by one 30ma RCBO?

Which part of the regs are you referring to, the 30ma is there to comply/protect the 16mm cable supplying each board and sockets in the rooms .. This will ensure my trip time of .4 seconds This would comply with the regs + keep mat costs down
 
Which part of the regs are you referring to, the 30ma is there to comply/protect the 16mm cable supplying each board and sockets in the rooms .. This will ensure my trip time of .4 seconds This would comply with the regs + keep mat costs down


Crack on then, don't come on here looking for futher solutions when it starts going wrong as it's evident you don't seem to want to learn anything.
 
Crack on then, don't come on here looking for futher solutions when it starts going wrong as it's evident you don't seem to want to learn anything.
Not really sure where you coming from.. The original post was about cost! But I would like to hear your views on what you think I'm doing wrong, does that setup not comply?
 