Mentor
Reaction score
247
How do you guys test a 110V tools transformer, I have never had occasion untill now, a local tradesman has asked if I would test his workshop and tools, I see no external earthing test point, so do I connect up the adaptor into an IEC and into the tester a Supernova, the tools I an check with the 110V outlet but the tranny has me flumoxed
Pict
 
i test the primary side as any appliance. then for earth bond connect earth lead to secondary E pin.
 
easiest way is to get an old 110v plug and connect a fly lead from the E pin sticking out of the plug.
 
Sometimes the screws that hold the top down will give you a another place to test .I believe you can buy a 110v test plug with an exposed test point at the rear ..if your feeling rich ..the 110v stuff i have tested has had a high rate of minor jobs needing doing to get a pass .Lots of cuts in insulation defectively plugs .no cover caps on the ext cables .I bet no ones offering this at less than a pound including repairs ...lol
 
Under a quid, I charge £1.60 for ammounts over a thousand items £1.85 normal and £40 minimum for bedsits staff accom etc
I know there are mobs out there doing 50p tests but, then again theres a lot of unemployment amoust clowns, cowboys and other circus acts
Pict
 
primary to transformer body 500v dc min
primary and secondary- its secondary may be centre tap earthed to body of transformer in an insulated container.
If not connected / or possible to disconnect secondary to lamination test between secondary and lamination-earth.
Also test as pat test. External cable other safety etc.
We test 4.5kv dc in flash test when manufacture.
Other test is give 240v input then output is above 110v eg115/120v depend on regulation.
you can use 1000v dc instead of 500v dc because all transformer has good insulation.
we connect low voltage to primary and measure secondary eg 23v to primary and measure secondary say 11v. secondary terminals to lamination is 5.5v
 

Reply to 110 tranny in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Replies
0
Views
242
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
319
Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
367
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
754
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock