According to the spec of that driver, it has "Built-in short circuit, overload, and over-temperature protection", so you don't need the breaker (presumably there to protect the old toroidal transformer from any short circuit of the track), assuming the house lighting circuit this is powered from has the usual breaker.12 volt lighting (rails) system. Replacing transformer (top) with LED version (bottom). Old one had circuit breaker (pictured on top of old transformer). Should I add a circuit breaker for the new?
View attachment 124210View attachment 124211
OP is in the US, where I don't think they have lighting circuits as such. Note that the old Tx has a 25A C breaker, which would be pointless on a 6A B circuit such as we're familiar with.assuming the house lighting circuit this is powered from has the usual breaker.
The 25A breaker appears to be on the 12V secondary side, and would presumably trip at around 300W+, which will only be an amp and a bit on the primary side. I just assumed it was for protection of the toroid!OP is in the US, where I don't think they have lighting circuits as such. Note that the old Tx has a 25A C breaker, which would be pointless on a 6A B circuit such as we're familiar with.
Looking at the pic at bit more closely, you're probably correct. The breaker is in a thick wire and the thinner white, black and green wires which aren't connected to anything are the colours for L, N and E in the US, IIRC. Didn't occur to me it might be on the output side.The 25A breaker appears to be on the 12V secondary side, and would presumably trip at around 300W+, which will only be an amp and a bit on the primary side. I just assumed it was for protection of the toroid!