Hi all. been to look at a job where power is required for a garage. need to go back and take a second look. but on first visit i noticed a fully loaded second consumer unit in the kitchen feeding a number of circuits,from a main consumer unit next to the dno cutout feed with 16 mm t+e. i'm assuming its just using the earth in the t+e as the main earth. is that acceptable or should there be a seperate earth say at 10mm. seen this in a number of flats so assumed to be ok but not comfortable with it. just looking for your views on this? Its a t-n-s set up by the way.
many thanks in advance Daz...
 
Chances are no not satisfactory, especially if main protective bonding relying on that 16mm cpc but you must confirm with Adiabatic equation as malc says
 