been reading up on CU's for the last week or 2 as im a bit of newcomer to the game,

I understand pretty much 70% of it all so far, but I the question in the title still stands... why is there 2 neutral bars?

Is it just so theres 'room' to add more circuits if needed, or is there another reason?

Thanks guys

Floody
 
if you`v got 2 RCDs..then you`l have 2 bus bars....and 2 neutral bars....its seperation so the RCDs dont conflict with each other.....to understand more about this then have a look at previous threads on the subject...including those about circuits with shared neutrals etc...
 
Thanks Sparks, I think I understand now.

Correct me if im wrong, but 1 RCD and say 4 circuits that the RCD looks after will sit on busbar #1 and neutral bar #1, and another lot of circuits on busbar #2 with the other RCD ? Its all about seperating the split load?
 
Thanks Sparks, I think I understand now.

Correct me if im wrong, but 1 RCD and say 4 circuits that the RCD looks after will sit on busbar #1 and neutral bar #1, and another lot of circuits on busbar #2 with the other RCD ? Its all about seperating the split load?
correct....
dont forget that if both RCDs shared the same neutral bar....the currents from each RCDs neutral would conflict the other RCD....don`t forget you can look at RCDs as a pair of scales....too much on one side tips the ballance....and the RCD lets go...
 
a split load RCD setup gives diversity......so, lets say you have several lighting circuits....you don`t want to plunge the whole house into darkness...so you can put the up lighting on one.....and the down lighting on the other...so if an RCD lets go...you will still have some lighting in the property....so you put the down lights on the same side as the up ring...and vice-versa.....so each floor will still have some power...table lamps and the like.....then theres the high integrity C/Us as well.....good for feeding garage subs and the like...
 