any body out there can explain to me how a 2 phase system works as its givin me a headache
 
do you have 2/3 of a 3ph or 2 x incoming singles or a 1ph 3 wire (2x singles inverted off the same transformer)?? More info reqd.
 
In the UK, two phase is most often found on construction sites, the 110V yellow transformers.
There will be 55V on each conductor, so although the wiring colours sugest that there is a Line and Neutral, in fact both conductors are phase conductors.
In the states, they often use a system where each phase is 110V, and for items of equipment that require 220V, they use two 110V phases.
The phases are generally 180° apart, as oposed to 3 phase where the phases are 120° apart.
 
Many village farms have a 480V split phase supply. Centre tapped transformer giving 2 x 240V supplies 180o apart.
 
It’s a common misconception that the secondary windings are at 180°. They are in fact vectorially added at 0°. At 180° the two windings would cancel each other out. Please see the drawing.
View attachment 10141
 
thanks gents but i am specifically looking to how it works on an offshore facility or a ship
 
Its the same as any three phase supply. You get 3 Phase conductors and a neutral. 400V between phases or 230V to earth. Where as in a "split Phase" system you get 2 phase conductors and neutral. 480V between phase conductors, or 240V to earth.

the centre tapping is taken to earth, which also acts as the neutral conductor.
 
sort of got it so the neutral is earth and at the fitting you have two line conductors is that right
 
any domestic TNC-S supply has a combined Neutral/Earth conductor, its just split at the meter head
 