pburley

Hi Guys

Popped round to a house today that as a TT earthing system. There is no gas or water bonbing and the main earth goes through the wall to a metal spike about 18 inches long in the ground outside. I will put all this right tomorrow but I was wondering what the 225 ohms on the ground floor ring would do to the MCB, eg will it work, flicking through my old text books now but was wondering what you guy think.

Many thanks guys.
 
The MCB won't trip in the required time as 225 ohms will exceed the maximum rating, however as murdoch mentioned the RCD, he did this because that will do the JOB, I like a reading under 100 ohms on TT, thats my personal choice however,and thats well well below the maximum reading allowed by BS7671. by the way whats bonbing?
 
Hi Guys

Popped round to a house today that as a TT earthing system. There is no gas or water bonbing and the main earth goes through the wall to a metal spike about 18 inches long in the ground outside. I will put all this right tomorrow but I was wondering what the 225 ohms on the ground floor ring would do to the MCB, eg will it work, flicking through my old text books now but was wondering what you guy think.

Many thanks guys.
Do the calc....simple ohms law....225 ohms will give you an EFC of 1amp.

How you gonna put it right then?
 
Hi Guys

Popped round to a house today that as a TT earthing system. There is no gas or water bonbing and the main earth goes through the wall to a metal spike about 18 inches long in the ground outside. I will put all this right tomorrow but I was wondering what the 225 ohms on the ground floor ring would do to the MCB, eg will it work, flicking through my old text books now but was wondering what you guy think.

Many thanks guys.
your going on about MCBs...
so whats an RCD for on a TN?...and whats it for on a TT?
 