M

m1ck_b87

Hi all

230v or 240v every time I measure voltage it's around 249v but you get stickers that say 230v or 240v so which 1 is it. I also know it fluctuates +5-5.
 
Bs7671 says 230v, you will get fluctuations as many things come into play, how close you are to transformer, load on network etc. but 230 is what it is now
 
Supply is still 240v really, but since harmonising with Europe we must use 230v for calcs.
 
A standard DNO transformer is 11/.433KV @ .45% reactance.

433V = 249.99V Ph to N

The DNO’s can lower the voltage but with the state of the networks the rise in current would most likely lead to failure.
 