Got a brainfreeze going on here, is it ok to use a 3 phase 3 pole rotary isolator to isolate a single phase instalation (l+n+cpc) hot tub circuit, i mean L1 as live, L2 as neutral and have L3 spare? :confused:

Thanks in advance..
 
Last edited:
No problem there.

I would suggest trying to label the L2 terminal as N though to avoid any confusion in the future.
 
Cheers for that Lenny, thought/hoping so, good point about labelling the terminal as well as just sleeving,

think i need a beer now after day i've had!!
 