Hi

When installing a 3 phase distribution circuit what determines the type isolator to use ( 3 or 4 pole ). In other words does the neutral have to be switched?


Cheers
 
Hi malcomsanford

The earthing system is a TT. As a matter of interest what isolators would i use for other earthing systems tncs, tns?
The installation is a distribution circuit 3 phase feeding a 2 way 3 phase dis board.

Cheers
 
If it is a TT supply then you will need to fit a 4 pole breaker as per reg 537.1.2

A lot of industrial/commercial equipment, especially rotating machines use regenerative breaking which requires the neutral not be isolated/switch
 
Just a thought what about if the service is tncs but you cant export the earth to another building so making that part of the system TT

Can you still use a 3 pole isolator at the service end?
 