lewlec

Evening all

any one know if I can use 1x 4-20ma transducer controlling 3 vsd's.... Paralleling them up???
greatfull for any info.

regards
gary
 
Yes you can, we use them for that purpose, but we use the PLC to give three seperate outputs to the VSDs.
 
You can buy splitters if you want to send the signal to more than one place, without using a PLC
 
Input to 1st
Output from 1st to control 2nd
Output from 2nd to control 3rd.

This will work fine until drive one or two develop a fault. Using a splitter, or a PLC to duplicate the signal will mean that you have redundancy.
Am I correct that this is for pumps, maybe a booster set?
 
Hi john
ye it's for a milking parlour, vacuum on demand. Three vsd's controlling three motors with one transducer. Any recommendations on transducers?
 
I think you would need three AO's. I take it your using integral control to control the pressure?
 
Last edited by a moderator:
You can use 3x signal isolators and loop the transducer 4-20mA signal through the inputs of each unit, then you can have an isolated output to each drive.
 