How can you go about this one, went to look at a job today at a fisheries with a big lake, the owner wants to put 3 x 750w aerators in the lake, along its length. The first run would be 200m, then about 100m to the 2nd one and then 100m to the 3rd one. I know you could probably step the cable size down between each one but surely you are still looking at minimum 16mm swa single phase, I get that to 11.2V drop. Is that how you would do it.
I reckon it would also be better to TT each one using a rod/RCD at each station so you could use 2 core cable (I doubt the SWA would be an effective earth at that distance but still connect the SWA through anyway. I don't do many oddball jobs like this normally.