How can you go about this one, went to look at a job today at a fisheries with a big lake, the owner wants to put 3 x 750w aerators in the lake, along its length. The first run would be 200m, then about 100m to the 2nd one and then 100m to the 3rd one. I know you could probably step the cable size down between each one but surely you are still looking at minimum 16mm swa single phase, I get that to 11.2V drop. Is that how you would do it.
I reckon it would also be better to TT each one using a rod/RCD at each station so you could use 2 core cable (I doubt the SWA would be an effective earth at that distance but still connect the SWA through anyway. I don't do many oddball jobs like this normally.
Have you calculated if the armour would be adequate?
It really makes no difference whether you use the armour or not it must still be sufficient to satisfy ADS so either way it must comply.
There is no reason to make it TT.
I would say cost wise it is cheaper to use separate runs, 2.5mm² to the first, 4.0mm² to the second and 6.0mm² to the third. Cost of cable using a quick tot up it is around the same but you don't have the cost for jointing the 16.0mm².
That sounds like a good idea, should be much easier to make off the ends, each one could gland straight into an outdoor spur or whatever we use to connect them, maybe just a commando socket actually.
Not sure about the SWA as the earth, just assumed it wouldn't comply over them distances, will have to work it out.
Cheers.
Redo the calculation for individual runs I think it is correct.
I have done now and all seems to tally up, I'm surprised 200m 2.5 comes in under the volt drop threshold, 6mm is fine upto about 450m as well.
Using TLC 16mm 3C SWA is about £4k for 400M, 2C is £2800 but using 3 individual runs 3C is £3100 and 2C is £2400 so decent saving plus as you say not needing adaptable boxes and such stuff to gland it all off into.
Thanks for the good idea.
would an installation like this come under section 705 (agricultural/horticultural premises), or general bs7671 rules regarding external influences, special earthing, and moisture ingress protection (IP ratings)?