Speak to the maker of your motors first of all. Chances are that the motors are actually suitable for both voltages and the maker can issue you with new data plates to cover the revised voltage.
As to running currents, for a motor running on 480V vs 460V, when running at the lower voltage the motor will draw a little extra current as to when on 480V (at the end of the day, the driven load still requires the same amount of power, so the motor has to work that little bit harder) - a 10 amp motor @ 480V will require 10.4A at 460V for the same driven load