(Upstream of the service head is the transformer, so I'll presume you've all been meaning downstream from the service head towards the DB;-)
4 single-cores or a length of XLPE? I'll answer my own question having read it again, it's only a couple of m so bound to be 4 cores clipped direct...
The "bus bar" from the service head to the iso, if the iso is mounted on top, has no real cable run (most people consider you need 0.5m to start calculating factors, so ignore it in this context). If you tried accommodating Reference Methods for connections like where an external iso is 35cm below the DB you always run into the issue that there's more cable inside the enclosures (iso, DB, whatever) when neatly dressed than there is on the wall between the items of switchgear, so you'd be declaring everything as B, "enclosed". If (like me) you're an OCD ADHD everything-out-of-the-book inspector then yes, on an EICR you can describe the connection as Ref B, which indicates to a person reading it the nature of the interconnect. (For instance I describe the internal tri-rated tails from a board iso to an RCCB as Ref B whenever it's appropriate to record the size of those internal tails, like in a domestic style "split load".) But in the context of cable calcs it's irrelevant, use C, "clipped direct", to get better values. There has to be enough cable to produce heat before you start worrying about it. Even solid bus bars in a panel sometimes have basic insulation, and it gets warm in there, but there'd have to be more than 0.5m of connection before I considered the Ref Method. (I had 24m of bus bar in a 1200A panel board once, that space got warm!)