What’s the rating for three phase 50mm PVC double insulated rails coming straight from the service head into an isolator sat directly on top of the head?

Can’t decide whether this is reference method B or not??
 
Hello

What’s the rating for three phase 50mm PVC double insulated rails coming straight from the service head into an isolator sat directly on top of the head?

Can’t decide whether this is reference method B or not??

Do you mean from the point of view of a cable calculation or to put on a report?

I am taking it you can't get a smoke wrapper between the service head and the isolator?

To be honest if that is the case I would be inclined (probably get some stick for this) to go N/A in the sense that there is no cable run. For there to be a cable reference method there needs to be a cable run of some sort.

If there is enough distance to get a cable clip in then I'd go with Refence Method C.
 
sorry, a cable calculation to answer your question.

The service head has 200A fuses installed but it has 50mm tails going into it stretching a couple of meters into a DB.

Looking to cut these back, terminate into an 160A isolator sat on top of the service head and then 70mm tails away from that in a trunking to a DB
 
sorry, a cable calculation to answer your question.

The service head has 200A fuses installed but it has 50mm tails going into it stretching a couple of meters into a DB.

Looking to cut these back, terminate into an 160A isolator sat on top of the service head and then 70mm tails away from that in a trunking to a DB

50mm tails seems to be a bit light for a 200A service head, is there anything upstream protecting them? I assume so because you have specified a 160A Isolator not 200A?

Is the reason to not renew the 50mm completely to avoid DNO involvement?

I take it space issue is why the isolator will sit directly on top the service head?

If the reference method is mucking up your cable calcs then I would just get the whole cable run renewed in 70mm if that satisfies the calcs.

Is this a supply to a Ryefield board for flats?

Sorry for so many questions just trying to understand the scenario.
 
It’s actually in what used to be a restaurant, now being made into another food premises.

To be honest we’d just renew the tails ourselves without the DNOs involvement for the ease of it.

They’ll end up asking a million questions and taking weeks to come out for what’s an half hour job.

There was no upstream downgrading to protect the cables. That’s why we’re looking to install the 160A isolator but in doing so, hoping we’ll be able to retain the 50mm tails.
 
(Upstream of the service head is the transformer, so I'll presume you've all been meaning downstream from the service head towards the DB;-)

4 single-cores or a length of XLPE? I'll answer my own question having read it again, it's only a couple of m so bound to be 4 cores clipped direct...
The "bus bar" from the service head to the iso, if the iso is mounted on top, has no real cable run (most people consider you need 0.5m to start calculating factors, so ignore it in this context). If you tried accommodating Reference Methods for connections like where an external iso is 35cm below the DB you always run into the issue that there's more cable inside the enclosures (iso, DB, whatever) when neatly dressed than there is on the wall between the items of switchgear, so you'd be declaring everything as B, "enclosed". If (like me) you're an OCD ADHD everything-out-of-the-book inspector then yes, on an EICR you can describe the connection as Ref B, which indicates to a person reading it the nature of the interconnect. (For instance I describe the internal tri-rated tails from a board iso to an RCCB as Ref B whenever it's appropriate to record the size of those internal tails, like in a domestic style "split load".) But in the context of cable calcs it's irrelevant, use C, "clipped direct", to get better values. There has to be enough cable to produce heat before you start worrying about it. Even solid bus bars in a panel sometimes have basic insulation, and it gets warm in there, but there'd have to be more than 0.5m of connection before I considered the Ref Method. (I had 24m of bus bar in a 1200A panel board once, that space got warm!)
 
Looking to cut these back, terminate into an 160A isolator sat on top of the service head and then 70mm tails away from that in a trunking to a DB
Sorry, I'm not doing well today, ignored your real question...
That looks like the safest solution. But does it need to be in trunking? Rather than buy 70mm and trunking and cut and mount it, can you order a couple of metres of 50mm XLPE and clip it? That's rated 179A...

6 & two 3's I suppose...
 
Hello, that’s for the reply.

I understand that there needs to be a minimum amount before you start using reference methods to calculate what detriment they have on a cable but if the cable length is negligible, there must still be a set current rating at which it’s considered to be OK.

Where would this figure come from?
 
Tables 4D (thermoplastic) and 4E (thermosetting), Apx.4 of the Bible somewhere in the vicinity of p450 (book not to hand), or Ap.F the OSG.
If you're doing proper, commercial cable calcs, you'll have the Design guide and of course it's in there also.

The most sensible beneficial Method is C in normal circumstances. Just don't pick E, "suspended in free air", because that's asking for trouble when all your switchgear is bolted to the wall ;-)
 
These cables aren’t clipped direct though which is why I though ref method B as they’re within an enclosure.

My thought was to take the figure from the BBB without adding any derating factors.
 