A plumber called me today and explained 3 days ago he went there and was reading 130v between bath tub and wet tiled floor on the 1st floor, drying out now and can't find 130v, and it's earthed through the Lead sheath TNS

- - - Updated - - -

Excuse me
.............
 
so....
when were talking MET...are we talking about the earth bar in the dis-board...or the MET (earth block)..if there is one..

if there is then check terminations in there...

and if the main bonding comes into that then i hope you didn`t drop the main earthing out of the earth bar for Ze...
 
With readings such as the 130v your plumber reported and even the 5 volts you're measuring you need to bear in mind that if a digital tester was used they're not very meaningful readings because of the astronomically high input impedance of the instrument.

Secondly if there was 130v a couple of days ago due to possible moisture having gotten into the floor and that figure has fallen dramatically now its dried out then it's reasonable to assume it might reduce to nothing in another few days. Maybe monitor the trend of the voltage over several days or even a week or so and go looking for a problem only if it isn't getting smaller as time goes by.
 
Im going to order an analogue meter in a minute and go and have a comparison, never came up against this before and has just thrown me

thanks
 
I've never heard of that term, by ribbon I mean the woven metal lace like connection between MET and sheath
 