Why? Isn't it obvious?

If there is a potential total load of 60amps and the MICC isn't fused correctly or on a 57amp fuse (god knows what size the fuse is, it's old) its either going to blow or catch on fire????

Of course I could just 'not worry' and just install the shower on a separate board, but that isn't the way I do things... I have a company and try my up most to do things correctly. If you guys seriously don't understand what I'm saying you should give up kitchen fitting and get an office job ;)
 
Why? Isn't it obvious?

If there is a potential total load of 60amps and the MICC isn't fused correctly or on a 57amp fuse (god knows what size the fuse is, it's old) its either going to blow or catch on fire????

Of course I could just 'not worry' and just install the shower on a separate board, but that isn't the way I do things... I have a company and try my up most to do things correctly. If you guys seriously don't understand what I'm saying you should give up kitchen fitting and get an office job ;)

Your the one who doesn't understand pyro and its ratings. But its all good, because your 'NICEIC'.
 
Oh dear.... You couldn't look in the regs book to find out the current carrying capacity of a cable. Clearly you can't grasp the concept of diversity. I have my doubts about you being able to screw back a socket. let alone attempt making an alteration on a board with pyro. And you have the audacity to criticise people on here. Hero
 
Erm I believe you were the one criticising ;)

The reason why I haven't looked it up in my book is because I'm on a forum instead? Diversity? There is none. If you looked at my 1st post you would see the circuits. It would clearly be under rated if the supply was around 57amps.

Thanks for your help.

I'm off now to make love to my GF. Have fun surfing the web and trying to make innocent by standers look like retards.

case closed
 
Erm I believe you were the one criticising ;)

The reason why I haven't looked it up in my book is because I'm on a forum instead? Diversity? There is none. If you looked at my 1st post you would see the circuits. It would clearly be under rated if the supply was around 57amps.

Thanks for your help.

I'm off now to make love to my GF. Have fun surfing the web and trying to make innocent by standers look like retards.

case closed

You seem not to have a clue about the workings of MICC cable, so why not give this job over to someone that does. You are correct on one statement, this job could well turn into a can of worms and cost you dearly, purely because you have no experience of MICC cable!!


Oh, and by the way, 6mm heavy duty MICC is more than capable of handling 60+A all day long!! lol!!
 
Oh really engineer?

I won't lie, I have only ever done one job with MICC. If I'm not sure about something I won't touch it.

My initial question was what load it could hold? And it's now spiralled out of control and people are assuming I haven't got a clue...
 
Hmm, can't see a problem with any of this.
Assuming twin and earth clipped direct, ok.(47A)
6mm MI would almost certainly be HD, so again ok.
Any thermal damage present? Unlikely
Lets not forget the shower has a fixed load, so no overload protection required. So providing fault protection is adequate leave it.
I wonder of you fully understand the characteristics of the protective devices installed, for instance the fusing factor?
How long does it take for a cable to reach its operating temperature? How long is the shower on for?

Regards

Cap
 
i had a question on this recently about what you would need to upgrade from a 7.2KW to a 9.2KW shower unit and its 10mm thermoplastic cable - 22m, 40amp MCB and a 50amp pull switch is this right?
 
Hey cap. As mentioned above I haven't really touched MICC in all my life, so I was a bit cautious in the size if the conductors.

the question isn't about the shower, this topic was aimed at the pyro.

michael
 
9.2KW = 37amps. Nearest MCB to 37amps is 40amps... The run is quite long 22M. Depending on the reference method used to install the cable with added correction factors then you will know if its done right.

bye the sounds of it it's done correctly.
 
Hey cap. As mentioned above I haven't really touched MICC in all my life, so I was a bit cautious in the size if the conductors.

the question isn't about the shower, this topic was aimed at the pyro.

michael

You mentioned CU changes i believe, all with MICC outgoing circuits (as i read it). You say you have experience of 1 MICC installation, ...what about refubishment of accessories on existing MICC installs??


As i say, (and i wasn't trying to be funny) if you don't possess the required experience of working with MICC cable then it is far wiser to pass this job on to someone that does know.


I've always allowed more CCC on MICC cables, (based on installation method) than those given in BS7671. In fact, most manufacturers data also give higher ratings too. But then i've been working with the stuff for the greater part of my working life, and that experience tells you things that books can't!! lol!!
 