Where do you stand on doing additions/alterations on sites where bonding is present but undersized? In this instance the bonding present is 35mm with 50mm required.

My understanding was that all bonding should be correct before any additions/alterations are done. This question has caused a big debate over the past few days with emails sent to the area manager of the NIC who has asked colleagues but has so far not come back to us with an answer.

I have been to this forum a few times for guidance but I have never posted before please be gentle with me :)
 
BS7671 states that for additions or alterations the (earthing and) bonding where required for the alteration or addition's safety measure must be adequate.

Unfortunately this is rather vague, how good is adequate?
The general approach to this is that is the earthing and bonding do not comply then they must be updated to the current wiring regulations.

However it is important to remember that there may be some circumstances where the boding is not relevant to the alteration or addition in which case it would not need updating.

There is also the consideration that if the existing installation has bonding that shows no signs of damage it may be considered that the bonding is adequate.

I am assuming you have a TNCS system with an incoming neutral >150mm2 which is why you need 50mm2 bonding.
This begs the question of why the bonding is not adequate in the first place, have no changes been made for some time?
 
It could and has been said that undersized bonding that has been in place for many years and showing no signs of heat damage could be safe for continued use, especialy if the alterations you are about to do would have negligable effect on the installation i.e extra loading etc.
vague area I know but i'm sure there is guidance to that effect ^^^^ well something like it anyway
 
well...this is the thing as well with ECRs....
TN-C-S earthing arangements...6mm CSA bonds....is it a fail?...well, if they show visible signs of damage then its a 2...if not... just note it....
 
Thanks for your responses,
This is down to a question I was asked the incoming tails/neutral to the property has been upgraded about 6 months ago to 2 x 300mm per phase/neutral. That is why all the bonding is now undersized because of this short time scale there is no visible damage to the bonding that I can see.
I am part of a team doing the PIR.
There are 7 blocks all steel construction with bonds gas, water, heating pipes and lightning protection.
So I have failed the bonded on all different categories because in some blocks I cant find the bonds.

Yesterday I was asked about the alterations work because of the nature of the site (it is a police hq) the buildings are constantly being maintained/upgraded/altered in some way. I can honestly say I was unsure because there main argument was is it worth spending £1000's of pounds upgrading what we have by 15mm so its nice to have a little feedback before I get hit with the questions again today.
Thanks.
(Forgive if this makes no sense it's early :snore: )
 