spud1

~
Arms
Hi guys,

I had a brain fog on the adiabatic.
Trying to ascertain suitability of a 6mm bonding conductor in a domestic installation. Doesn't help that I forgot my regs book too!

I have a pefc of 1.17KA. Can anyone help please?

Thanks.
 
Quiet this morning!
My thoughts were that if I could prove minimum size of the main installation earthing conductor and then use the 50% rule for the main bonding conductor it might come out at <6mm. Although I have just noticed that the installation has TNCS earthing! Does this mean I can't calculate and have to select from table??

Any help please?
 
It needs to comply with table 54.8, the adiabatic is not for sizing protective bonding conductors
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
on a TNC-S installation min. size for bonding conductors is 10mm.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
We're doing remedials at this installation, including a consumer unit upgrade. The route for rewiring the bonding conductor is unbelievably difficult! Is there any way I can risk assess to get around rewiring this 6mm bonding conductor? ?
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...

I think you are talking about the test to prove whether an item is an extraneous part or not.
 
IR test. pipe to MET. if >22kOhms does not need bonding.
 
main bonding protective conductors are sized by the Relevant table in the IEE REGS, not by adiabactic equation.
i just use whatever i find first on the van. still got a roll of plain green. (imperial). think it still has the price on the 100 yard drum.... £1.10.,6d.
 