When plotting your PEFC against the times for your protective device in appendix 3 and your trying to work out an exact time, is it better to round it off to the nearest higher time frame?....As this will give you a slightly higher csa when working out your min acceptable size, which is better than selecting a lower time frame. I haven't carried out this equation recently.

Any replies would be appreciated.
 
depends how slow the device operating time is.

around 0.5 secs or less theres hardly any difference in the final figure.
nearer 5 secs i'd be using the exact graph time line.
 
yes...do your PFC....
check that against the time current tables in your book...then if your still good...its PFC squared X 0.4=
you apply the square root to the answer to the above....

- - - Updated - - -

depends how slow the device operating time is.

around 0.5 secs or less theres hardly any difference in the final figure.
nearer 5 secs i'd be using the exact graph time line.
but its 0.4 AND 5 secs now in the BGB biff..
 
Cheers Biff.... Ive just been going through cable calcs recently as I'm a bit rusty with certain bits and I just wanted to make sure I was right.
Thanks for the reply anyway :-)
 
yes...do your PFC....
check that against the time current tables in your book...then if your still good...its PFC squared X 0.4=
you apply the square root to the answer to the above....

- - - Updated - - -

but its 0.4 AND 5 secs now in the BGB biff..

If your time worked out to be roughly 0.35s but you wasn't 100% sure would you shift upto 0.4s rather than the other way? I would shift up to the higher time....
 
Your time is obtained from the graphs in the BGB as different devices have different characteristics at the measured fault current.
 