Hi all. So I have been asked to install a couple of 18th century antique chandeliers that have previously been ‘electrified’ (customers words!).
Anyway I am but uneasy about it in terms of earthing. There is the kind of 2 core cable you sometimes get with modern double insulated pendants lights, and the cable feeds plastic e27 lamp holders around the chandelier. The cable is tied to the metal frame with thin tie wire.

Physical check and all is fine. I would have preferred to get an earth down to the frame - but can’t.

Obviously no double insulation symbol.

Am I being over-cautious? Would you put it up as is?
 
I cannot see it properly , but if it is metal I would want it earthed.
I would not put it up as it is .
Maybe there is a way to get a similar 3 core in.
I would be careful with this as the alterations will be your responsibility.
 
Last edited:
Can you put up pictures of the fitting so we can see it more clearly? If it were me I'd be similarly cautious and would likely want to drill through it at some point to fit an earth, unless it really is crystal clear that all the metalwork is separated.
 
Can you put up pictures of the fitting so we can see it more clearly? If it were me I'd be similarly cautious and would likely want to drill through it at some point to fit an earth, unless it really is crystal clear that all the metalwork is separated.

I took a few photos but they were all pretty poor. I was trying to keep the light in its transportation box....
 
Yeah, that's fair... I can also see why drilling through an antique light fitting might be considered a bit uncouth unless absolutely necessary!

Exactly.

There are some tiny bolted connections in the structure with what look like hand cut nuts ?!

Not for the faint hearted trying to get an earth to it - and it will always be visible if I went down that route. A nice bit of green and yellow on a chandelier?
 
put in a three core cable .Transparent Round Clear PVC 3core 6A Electric Flex Cable Chandelier CCF-534 0.75

Thanks Buzz. I’m wondering how to work that though - as the lamp holders are plastic with two terminals.

There are a couple of specialist companies that ‘electrify’ antique chandeliers. I am wondering what they use - but I suspect it’s 2 core double insulated for plastic lamp holders or 3 core for metal lamp holders...
 
Another problem with connecting an earth to this type of fitting is they are very often multiple metal parts with unreliable physical connections between the parts. Earthing at one point is no guarantee the entire construction is effectively earthed.
 
Thinking it through and considering that;

1. The wiring looks to have been professionally done, and is correctly terminated and secure in plastic lampholders with no inner insulation showing.

2. Cable has only been lighting secured to the frame with ultra thin tie wire with no damage to the sheath/outer insulation.

3. Circuit is RCD protected.

4. There is no known local infestation of gymnastic flying squirrels able to reach high ceiling heights to chew cables (no external influences).

Then I'm inclined to install them as is....
 
Thinking it through and considering that;

1. The wiring looks to have been professionally done, and is correctly terminated and secure in plastic lampholders with no inner insulation showing.

2. Cable has only been lighting secured to the frame with ultra thin tie wire with no damage to the sheath/outer insulation.

3. Circuit is RCD protected.

4. There is no known local infestation of gymnastic flying squirrels able to reach high ceiling heights to chew cables (no external influences).

Then I'm inclined to install them as is....
get them fitted, then learn how to spell chandelier. :D:D:D:D.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Antique Chandalier - with no earth...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
Marcus Vaughan,
Replies
20
Views
2,967

Advert

Back
Top