C
| watts where stated | 60w x 3 |
| Ib design current | 1.30 |
| In device rating and type | B6 MCB BS 60898 |
| Reference method | METHOD B |
| Ambient temp in ◦c | 40◦c |
| Cable type/ insulation | 90◦c Thermo setting Single core non sheathed cables |
| Ca ambient factor | 0.91 |
| Cg grouping factor | 0.80 |
| Length in meters | 12.5 METERS |
| Max volt drop | 6.9 |
| mV/A/m max | 31 |
| Size selected mm2 | 1.5MM² |
| It | 3.41 |
| Iz(must be larger than In) | 0.61 |
| Actual voltage drop | 0.27V |
| Max disc time | 0.4 |
| ACTUAL Zs | 0.18 |
| Max Zs as bs7671 | 0.35 |
Done it red for you
watts where stated 60w x 3 180w Ib design current 1.30 0.78A In device rating and type B6 MCB B6 RCBO 61009
BS 60898Reference method
METHOD Method B
BAmbient
temp in ◦c40◦c 40c Cable type/
insulation90◦c
Thermo 90c T/S single core
setting
Single core non sheathed cablesCa ambient factor 0.91 0.91 Cg grouping factor 0.80 0.80 Length in meters 12.5 METERS 12.5 Max volt drop 6.9 6.9 mV/A/m max 31 31 Size selected mm2 1.5MM² 1.5mm2 It 3.41 8.24 Iz(must be larger than In) 0.61 23A Actual voltage drop 0.27V 0.3v Max disc time 0.4 0.4s ACTUAL Zs 0.18 0.497 round it off to 5 ( using a Ze of 0.11 ) Max Zs as bs7671 0.35 7.28 x 0.8 = 5.82