Any way to utilise the 6mm earth in the EVCP cable for gas Main bonding?

HappyHippyDad

~
Arms
Supporter
I'm certain there won't be any clever ways of doing this, but...

I need to get a 6mm EV ultra cable to a charge point (35m run from the meter)

There is no Main bonding on the gas, so I need to get at least a 6mm to that (TT earthing).

The gas meter is only 1m away from the EVCP. Is there anyway of utilising the 6mm earth in the EV ultra cable as the main bonding for the gas?
 
Are you running a SWA EV ultra, if so the armour will provide much more than a 10mm copper equivalent CSA as well as the 6mm core itself.

Would need to calculate continuity but it may work at less than 0.05 ohms

Would be tempted to buy these new snazzy SWA glands and earthing nuts to belt and brace it.
 
Are you running a SWA EV ultra, if so the armour will provide much more than a 10mm copper equivalent CSA as well as the 6mm core itself.

Would need to calculate continuity but it may work at less than 0.05 ohms

Would be tempted to buy these new snazzy SWA glands and earthing nuts to belt and brace it.
Thanks for that BE.
The reason I'm getting confused is I asked AI !!
It gives such conflicting advice and was adamant I could not use the CPC inside an EVCP cable as a Main Bonding cable.
It wouldn't be SWA.

The plan would have been to fit an IP box near by the EVCP in which I could terminate the EVCP cable and from there take a 6mm conductor to the gas. I'm just not sure if this is compliant with the regs or even safe now that I've asked AI
 
Happens all the time. Run a supply to an outbuilding which happens to require main protective bonds and the CPC of that supply also supports the main protective bonding. In my example it would normally go to a distribution board so it is never really questioned as the bonds become separate from other CPCs downstream but the principle is the same. Not sure you will find an outright answer as it would be an unusual practice but if you were to install a small distribution board at the charger I doubt you would question it. Can't you run a separate bond with the cable you are putting in or is it external. You could always change to a four core and utilise the green/yellow as the bond.
 
Happens all the time. Run a supply to an outbuilding which happens to require main protective bonds and the CPC of that supply also supports the main protective bonding. In my example it would normally go to a distribution board so it is never really questioned as the bonds become separate from other CPCs downstream but the principle is the same. Not sure you will find an outright answer as it would be an unusual practice but if you were to install a small distribution board at the charger I doubt you would question it. Can't you run a separate bond with the cable you are putting in or is it external. You could always change to a four core and utilise the green/yellow as the bond.
Thanks for your thoughts @westward10
The EVCP CU will be going very close to the meter box in order to make sure the tails from the henley block are as short as possible as there will be no fault protection (there will be about 700mm of tails).
I could run a separate 10mm conductor alongside the EVCP cable, but this is what I was trying to avoid, as it is a 35m run around the outside of the house and I have a 6mm CPC in the EVCP cable going almost to the gas meter. Why the worry if it is external?
I did think about a separate core in the EVCP cable, but it is EV ultra cable (with a cat5e in it for the CT clamp), so I doubt they make a 4 core, with data. oo.. I bet they do a 5 core. i'll have a look
 
I just thought running a green/yellow externally would be it need protection from UV damage.
 
I just thought running a green/yellow externally would be it need protection from UV damage.

There are many installations where G/Y is run externally... between metallic enclosures, structural.... I am thinking building site portacabins....

I think its only grey T&E sheath that is affected by UV.... Black pvc on the outside of SWA is fine... Just a different type of plastic
 
Well, I have to admit I have run green/yellow earth or Main bonding a few times externally and perhaps have not given it enough thought.
I never run grey twin and earth externally and usually give the obligatory tutting sound to the customer when I see it. Perhaps other electricians are giving my externally run bonding a bit of a frown!
 
Well, I have to admit I have run green/yellow earth or Main bonding a few times externally and perhaps have not given it enough thought.
I never run grey twin and earth externally and usually give the obligatory tutting sound to the customer when I see it. Perhaps other electricians are giving my externally run bonding a bit of a frown!
I run black 10mm externally, with black metal Linian clips, and over-sleeve with green/yellow at each end.

If the sun ends up degrading the black to such an extent that the bare copper is exposed, what's the worst that can happen? "Oh noes! An extraneous conductive part! Just like... all the other extraneous conductive parts...."
 
Thanks for your thoughts @westward10
The EVCP CU will be going very close to the meter box in order to make sure the tails from the henley block are as short as possible as there will be no fault protection (there will be about 700mm of tails).
I could run a separate 10mm conductor alongside the EVCP cable, but this is what I was trying to avoid, as it is a 35m run around the outside of the house and I have a 6mm CPC in the EVCP cable going almost to the gas meter. Why the worry if it is external?
I did think about a separate core in the EVCP cable, but it is EV ultra cable (with a cat5e in it for the CT clamp), so I doubt they make a 4 core, with data. oo.. I bet they do a 5 core. i'll have a look

I believe the bonding conductor needs to be continuous (this might just be best practice but always thought that to be true) so that rules out using the CPC.

Like you said though they don't do a four core in EV Ultra so it would have to be 5 core you could then loop a core in and out of the IP box to the gas bond in one continuous piece.
 
I believe the bonding conductor needs to be continuous (this might just be best practice but always thought that to be true) so that rules out using the CPC.

Like you said though they don't do a four core in EV Ultra so it would have to be 5 core you could then loop a core in and out of the IP box to the gas bond in one continuous piece.
There is no requirement in BS7671 for them to be continuous and it wouldn't be no different to connecting from a board on a submain.
 
There is no requirement in BS7671 for them to be continuous and it wouldn't be no different to connecting from a board on a submain.
I cannot remember where I picked this up probably was in an OSG? A quick google search suggests it is in BS7430.

You will see it when a single bonding cable is used for Gas and Water the first clamp will not have the Bonding conductor cut. I believe the reasoning is that if the an intermediate clamp is removed for any reason the bond will still be intact to the remaining.

Funnily enough I came across this just a few days ago, Gas meter was relocated to outside, bonding cable which went on to the water was left disconnected but was not cut so the bond remained in place for the water.

I think connections inside a board would be deemed only accessible by competent persons. I guess you could argue that would apply to the IP Box also.
 