Sorry E54 I was being a bit harsh on the DNO’s, I was commenting on the chances of them tidying up the their installation on the pole.

That transformer has me puzzled, the LV is classic for three phase 4 wire. I have seen some transformers where a standard tank is used and blanks fitted to unused bushings.
 
Right chaps, back from the brink......was talking to a Western Power design/engineer/planner on the phone earlier who had the lines up on her screen.....seems the guys who attended site either didn't know their arses from elbows (and, you know what? I REALLY hope it wasn't that!!) or just spun me some line because they couldn't be bothered. So: as far as WP are concerned, the overhead HV side is 3 wire 3ph and the LV output is separate L, N, E. Hence why it's been presented as TN-S at the intake.

On another note, it's not looking good for the connection of a ground source heat pump off that line!! :(
 
Yes, it's not definite yet, but she advised me 'not to do much more' at the moment!! I'm NOT looking forward to that particular conversation with the client........

I think the concern is more about harmonic disruption back on to the overhead network rather than a loading one. The specified Flicker standard on that particular pump is the worst one, apparently. Don't know much about flicker so will take her word for it!
 
Last edited:
And the latest development is.......

WP have just realised that it's only a 15kW transformer. The harmonics they can deal with, even all the other motors and pumps I'd overlooked telling them about isn't going to phase them. But shear numbers of amps will!

The planning engineer and I have finally agreed a figure of 98A as a 'working load' (given that the after-diversity calcs are about 150A).

Cost to upgrade the pole transformer: £4.5k and the client will have to move to whole-current metering which is also likely to smart a bit! Lead time is 6-8 weeks. Client wants to move-in in four.........
 
I've still got a call booked for a planner to attend site anyway due to loading issues (AFTER diversity, and even with a pinch of fairy-dust hope and fingers crossed my calcs are running at 140A, almost half of which are on continuous duty - on an 80A head [mis-labelled as 100A]).
I can't see you getting a 100A supply, with a Ze of 0.67Ω.
In fact I'm suprised they allowed 80A, you sure it's not 60A?
 
spin - its all irrelevant now, but I know for certain its an 80A 1361 as I took the carrier apart! And no, the DNO don't want to come and arrest me!!!!
 