You need a copy of GN 3 for the answer to the first question as I said in my previous post.
 
A IR result of 1.95MΩ could mean that a latent defect exists. Therefore each circuit should be tested separatly as this will help to indentify whether one particular circuit in the installation has a lower IR value, which possbly indicates a latent defect that should be rectified or whether the low resistance represents the summation of individual circuit IR and as such may not be a cause for concern.
 
All i can see is the output values and the acceptable vaules of an IR tester but nothing to say why these values are so other than leakage current durring normal conditions but thats referring to extraneous condictive parts
 