Rich408

My first Post....

My thought and would welcome others.
- My recent experience made think how can this be correct...

Install type that was in place - 3 phase -ali shaped cores - copper armoured - no neutral conductor - Using the Copper as n/e combined.
CSA-185mm- 3 poles.
CSA - 50mm- N/E.

My point is- high ampere rating of The 3 poles - infact Ali shaped is good - As for the Harmonic Effects which the N/E may be to much for the CSA-
As one phase goes into different Harmonics then the Heat generated would impact the rated value of N/E.
When this happens surely the 2 other poles would suffer,so how could it correctly deal with a Fault.

I can say this if the install starts at a 2500 KVA sub-Hv>LV with up to 12 feeds to DB's Each one demanding underload 700 ampere.The cables Bunched/trenched/ connected to the DB's located in High humid/Temps get high to 80 odd the Impacted heat would also have an impact on the rated value of cable.

I do understand the % of load may differ - Small amount allowed-what happens when the EOL Units connected go into fault-
The effects would have a massive impact.
 
I did not know they made copper armoured cable, are you sure it is not concentric!
However the minimum neutral csa you could get away with (without harmonics) is half the size of the line conductors and with a copper equivalent of 110mm² line you do not have half the size on the "armour", with harmonics messing things up you would need an equivalent csa the same as the line.
 
Last edited:
The combined N&E on a copper armour does sound a little odd to me as well. I'd need to dig out some info to be sure but i think if it's a split concentric the neutral has a higher current rating than the individual phases... It's not a cable we often come across TBH.
 
Never seen or heard of such a cable make-up?? Any chance of a photo or two??

As has been correctly stated, reduced neutral multi core cable will be half the phase/line conductor size. You don't see them used as much these days, as the increase in IT equipment and other detrimental loads, precludes their use. The old regional electricity boards used to used them extensively, and are now paying the price on initially saving a few pennies in the past... lol!!
 
Rich, you need to give the specification of the cable. Without further information no one can help.

I’ve run rather a lot of 185 3½core, I can assure you the ½ core is 95mm².
 
My first Post....

My thought and would welcome others.
- My recent experience made think how can this be correct...

Install type that was in place - 3 phase -ali shaped cores - copper armoured - no neutral conductor - Using the Copper as n/e combined.
CSA-185mm- 3 poles.
CSA - 50mm- N/E.

Are you sure you have a TNC-S (PEN/CNE), is this UK?

My point is- high ampere rating of The 3 poles - infact Ali shaped is good - As for the Harmonic Effects which the N/E may be to much for the CSA-
As one phase goes into different Harmonics then the Heat generated would impact the rated value of N/E.
When this happens surely the 2 other poles would suffer,so how could it correctly deal with a Fault.

You stated balanced load, so all the phases will be producing the same level oh harmonic distortion as the others?

What harmonics are present?

I can say this if the install starts at a 2500 KVA sub-Hv>LV with up to 12 feeds to DB's Each one demanding underload 700 ampere.The cables Bunched/trenched/ connected to the DB's located in High humid/Temps get high to 80 odd the Impacted heat would also have an impact on the rated value of cable.

It all depends upon the Harmonics present, Frequency effects Inductive reactance, then you have to consider the skin effect and the proximity effect.

I do understand the % of load may differ - Small amount allowed-what happens when the EOL Units connected go into fault-
The effects would have a massive impact.

I don't really understand what your asking, and your extremely vague with something which is complex, you will not get the answer i'm afraid.
 
Last edited:
I did not know they made copper armoured cable, are you sure it is not concentric!
However the minimum neutral csa you could get away with (without harmonics) is half the size of the line conductors and with a copper equivalent of 110mm² line you do not have half the size on the "armour", with harmonics messing things up you would need an equivalent csa the same as the line.

I've seen the armour of a cable to be 1/3 copper, was used quite often in quarries. Never seen a full copper armoured cable though, do you have any photos?
 

Reply to Balanced loads-harmonic effects. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hello everyone. Budding DIY enthusiast fascinated with how things work - and, to a lesser degree, fixing things that are not working. I suppose my...
Replies
0
Views
1K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock