Hello

So had to add a new socket at a customers house today in an old kitchen extension, for fridge and washer.

Flat roof, concrete floors, no other sockets on that side and they didn’t want any chasing etc, so outside route it was back to the board.

Obviously can’t use twin and earth outside without some form of UV protection, so I went with 2.5mm 3-Core HO7RN-F (was out of reach and unlikely to ever get damaged). 16A RCBO, with the option to upgrade to a 20A if the fridge is replaced with a drier.

Got it looking pretty neat in the end but with such a chonky cable I was thinking surely there must be a better choice?
And I don’t know what it is but HO7RN-F always sags between cable clips without an excessive amount (or there’s some trick I don’t know of).

What would you use / do?

If time was permitting I’d have probably gone conduit route as I usually would but it wasn’t this time.

Overthinking this but I like my cabling nice, neat and discrete and I just wasn’t happy. Customer thought it was great haha but you know what I mean.

Hope everyone’s having a great Friday night anyways 😂 I should get out more…
 
Hello

So had to add a new socket at a customers house today in an old kitchen extension, for fridge and washer.

Flat roof, concrete floors, no other sockets on that side and they didn’t want any chasing etc, so outside route it was back to the board.

Obviously can’t use twin and earth outside without some form of UV protection, so I went with 2.5mm 3-Core HO7RN-F (was out of reach and unlikely to ever get damaged). 16A RCBO, with the option to upgrade to a 20A if the fridge is replaced with a drier.

Got it looking pretty neat in the end but with such a chonky cable I was thinking surely there must be a better choice?
And I don’t know what it is but HO7RN-F always sags between cable clips without an excessive amount (or there’s some trick I don’t know of).

What would you use / do?

If time was permitting I’d have probably gone conduit route as I usually would but it wasn’t this time.

Overthinking this but I like my cabling nice, neat and discrete and I just wasn’t happy. Customer thought it was great haha but you know what I mean.

Hope everyone’s having a great Friday night anyways 😂 I should get out more…
I'd be using the same as you.. H07RN
I'd be interested to know what peoples thoughts are on using black H05VV though (assuming unlikely to be damaged)?
I remember many years ago @Richard Burns talking about this, and I 'think' he said something along the lines of black rubber cable first, but he couldn't really see an issue with black PVC. I do apologise to RB if I am miss-remembering though.
 
Last edited:
I use H07RN-F, or T&E in PVC conduit (but that's even chonkier). For outside lights, I've been known to use H05RN-F. If it needs to be white (e.g. outside lights on a rendered house), I use FP200 Gold (manufacturer's datasheet states, "Suitable for outdoor installation with exposure to normal daylight UV").

Re the sagging between the clips on H07RN-F, I use the metal Linian clips, and pull the loose end of the cable as I knock the clip in, so it doesn't sag. Usually looks pretty neat.
 