K

keniff

hi guys i know its late, but... if you are trying to work out whether you need to bond an extraneous conductive part is this correct -

R<50v/Ia in my case its on a rcd so....

R<50/0.003 = 16.666

so if its under 16.6 M ohm it needs to be bonded? thanks
 
I had that in my head but can't get that answer from the formula, could you let me know how you get 22 cheers glen
 
Extract from the voltimum site
Chapter 6 of IEE Guidance Note 8 (Earthing & Bonding) details that where the designer elects to accept the let-go threshold of 10mA as a safe level and where the resistance between the conductive part concerned and the Main Earthing Terminal (MET) is above 22kohms, the conductive part need not be considered to be an extraneous conductive part which introduces an earth potential as defined in BS7671 and would therefore not require main protective bonding.​
 
Last edited:
Extract from the voltimum site
Chapter 6 of IEE Guidance Note 8 (Earthing & Bonding) details that where the designer elects to accept the let-go threshold of 10mA as a safe level and where the resistance between the conductive part concerned and the Main Earthing Terminal (MET) is above 22kohms, the conductive part need not be considered to be an extraneous conductive partwhich introduces an earth potential as defined in BS7671 and would therefore not require main protective bonding.​

Hi Kieth, You may be wondering how Richard's quote has been derived, particularly as the NICEIC tend to muddy the once clear water by quoting a different figure of 7k Ohms instead of the traditional figure of 22k Ohms.

NICEIC Value:
The metallic part can be assumed not to be an extraneous-conductive-part if the following condition is met:
Rcp> (Uo/Ib) - Ztl
where,
Rcp is the resistance between the conductive part and the MET in Ohms
Uo is the nominal voltage to Earth in Volts
Ib is the value of current through the body in Amperes that should not be exceeded. (The value may be taken as 30 mA for a disconnection time of up to 0.4 s, as given in DD IEC/TS 60479)
Ztl is the impedance of the human body in Ohms. (The value suggested in DD IEC/TS 60479 is 1000 Ohms where Uo is 230 V (50 Hz) under dry or wet conditions.)

Taking Ib as 30 mA and Ztl as 1000 Ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:
Rcp > (230/0.03) - 1000
Rcp > 6667 Ohms (Rounded Up by NICEIC to 7k Ohms)
Thus in this case, if Rcp exceeds 6,667 Ohms, the pipe may be considered not to be an extraneous-conductive-part, such that main bonding of the pipe is not required.

Traditional Value:
Traditionally most electricians have preferred to err on the cautious side and use a 10mA value of current through the body in amperes (the so called let-go threshold) that should not be exceeded, which changes the result of the formula to 22k Ohms.
 