Hello all,
Just after some advise please!
The company who I work for previously undertook an electrical installation on a caravan park. This was about 3 years ago now back in 2023.
Now they have just had another contractor come in to undertake the 3 yearly electrical installation condition report on the underground cabling.
They have picked up the following issue;
BW brass cable glands have been used on the SWA to each external connection unit and given a C2 for every single one of the 100 plots.
There is a few pictures we have received which show a bit of oxidisation between the gland and armouring of the SWA but this may have been moisture in the box rather than the gland itself and isn’t every box from our conversations with the manager.
After looking at the manufacture specification for the glands they actually do suggest for indoor use as they give no IP rating against external influences.
We are waiting for the report to be sent through so it can be reviewed in more detail but the earthing system is TT with upfront RCD protection and all maximum measured Zs values are well within permitted limits.
Would this warrant a code 2 or any supporting regulations to back this up?
Thanks all.
Just after some advise please!
The company who I work for previously undertook an electrical installation on a caravan park. This was about 3 years ago now back in 2023.
Now they have just had another contractor come in to undertake the 3 yearly electrical installation condition report on the underground cabling.
They have picked up the following issue;
BW brass cable glands have been used on the SWA to each external connection unit and given a C2 for every single one of the 100 plots.
There is a few pictures we have received which show a bit of oxidisation between the gland and armouring of the SWA but this may have been moisture in the box rather than the gland itself and isn’t every box from our conversations with the manager.
After looking at the manufacture specification for the glands they actually do suggest for indoor use as they give no IP rating against external influences.
We are waiting for the report to be sent through so it can be reviewed in more detail but the earthing system is TT with upfront RCD protection and all maximum measured Zs values are well within permitted limits.
Would this warrant a code 2 or any supporting regulations to back this up?
Thanks all.