Hi all,

Did a eicr today and found a mains extract fan in zone 1 also with no 3 pole isolator.

I was going to put under a c1 as its pretty much next to the shower head but then c2 maybe applicable.

Just wondering what you guys would put.

Thanks in advance

Ashley
 
If its in zone 1 then surly it such be a 12volt and not mains fed never mind there being no isolator. Plus have you taken the ip rating into account?
 
Hi all,

Did a eicr today and found a mains extract fan in zone 1 also with no 3 pole isolator.

I was going to put under a c1 as its pretty much next to the shower head but then c2 maybe applicable.

Just wondering what you guys would put.

Thanks in advance

Ashley

Any idea of when it was installed? Is it wall or ceiling mounted?

If its in zone 1 then surly it such be a 12volt and not mains fed never mind there being no isolator.

Allowed by 701.55 as long as it's designed for that location.
 
Hey,

The bathroom has been Newley installed and moved around slightly, speaking the the person who did the bathroom he tells me that the fan was always there it's just the bath and shower have been moved (asked who moved the shower - an electrician did it, yeh right) anyways so the fan originally wasn't in a zone but is now, the fan is ipx4 but like I say mains and I was going to put down a c1, and unsatisfactory...

Cheers for the replies
 
For me that would be a C2 but I don't know the exact location of the fan in relation to the shower and zone, IP rating could be suitable unless it can come into contact with jets etc. Is there RCD protection?
 
The shower head I level with the fan and aprox 4inch away and yes RCD protected,

Thanks for all ur input
 
As spin says, ventilation equipment is allowed in zone 1, being IPx4 it is also suited to the area.
 
You could make a comment on the lack of an isolator if there is no source of outside light in the bathroom, otherwise it's fine.
 
Ok all,


Thanks for all the advice,

Put the isolator as a recommend and suggested to change to SELV fan for any future modifications and they have gone ahead with it so all being its going to a 12V..

Cheers

Ash
 
12v is not required! As said above.
Unless its in zone 0 lol.
As for isolator, if there is light to allow for maintenance to be done there is no requirement,
No code needed.
 