When you are detremining the length of a RFC what exactly is its length, is it the total amount of cable you will use or the amount you will use divided by 2?
Total length , ie , end to end measurment.
Oh, so if its say 20m to the furthest point of the circuit, the length i use for the cable calculations is 40m.
YES
And one more question, while im on the subject, on a lighting circuit do you include all the cable drops to all the switches or just the distance to the r1+r2 point?
Ignore switch drops , just measure from consumer unit to the fitting furthest away , or as you say , the R1+R2 point