Hi guys; I have a customer who has a chimney that's been capped off (with concrete I beleive), such that it is no longer usable as a chimney, and he states it never will be again. I need to run a cable, and route 'A' would be a cpmplete ball-ache, whereas route 'B' would be to use the chimney as a riser, and it would make the install much simpler. My concern is whether this is acceptable, as someone in the future may want to put the time and effort in to re implementing the chimney. At that point in time, does that just become a case of 'that's then their problem', or is this fundamentally unsound practice? Any advice greatly appreciated!
 
In some ways, it is kind of the next guys problem if they want to uncap the chimney and put it into service.
however, the issues that you have are,

1. soot (especially from coal fires) is highly acidic.
you may have to use a cable that is resistant to acids or run pvc inside polypropylene conduit.

2. support
how are you intending to support the cable as it goes down the chimney, most cables are not suitable to be hung a long distance and should be supported along there length.

3. Installation
disturbing a build up of soot is bad, if it gets into the room below then there are health hazards and also clean-up may be difficult or impossible without professional help.
also pulling a cable through a brick built chimney may damage it where you cant see it, if there are any sharp edges in there.
 
In some ways, it is kind of the next guys problem if they want to uncap the chimney and put it into service.
however, the issues that you have are,

1. soot (especially from coal fires) is highly acidic.
you may have to use a cable that is resistant to acids or run pvc inside polypropylene conduit.

2. support
how are you intending to support the cable as it goes down the chimney, most cables are not suitable to be hung a long distance and should be supported along there length.

3. Installation
disturbing a build up of soot is bad, if it gets into the room below then there are health hazards and also clean-up may be difficult or impossible without professional help.
also pulling a cable through a brick built chimney may damage it where you cant see it, if there are any sharp edges in there.
Hi James. Really appreciate your thoughts, and I will certainly discuss all this with the customer; I must admit the first thing that came to mind was how to achieve adequate support, but potential attack from soot is a very valid point. Once again, many thanks for the advice 👍
 
Once you've drilled a hole into a chimney soot will come out, and it will never stop.
Even once you've filled around the cable soot, or at least a black stain, will keep reappearing.
 
Last edited by a moderator:
Once you've drilled a hole into a chimney spot will come out, and it will never stop.
Even once you've filled around the cable soot, or at least a black stain, will keep reappearing.
Hi Brother Blue; thanks for the info, and I think I'll be reconsidering the cable run due to all the above advice. 👍
 
In addition, the purely mechanical part is annoying in way I don't find trivial: drilling hard dense fire brick is not like drilling a regular engineering brick. You'll want to use a decent new SDS bit and then the opposing face will likely blow exposing the inner material. Not a problem hidden inside the disused chimney unseen and unlikely to be exposed to moisture, but potentially leaving jagged spikes exactly where the cable is exiting and drawing down to the surface.
 