Doing a PIR this morning, TNS, 16mm clamped to supply cable which leads to the MET, <100v between L&E so couldnt get Ze, there is a 6mm Earth running from the MET to the 3036 board, despite the non existent Ze if i test between the MET and line I get 240v and 0.23ohms!, there is no bonding at all, loop between L & N is 0.10ohms
Ive already phoned this one in
It may be that the Earth is not connected or there may be a voltage present.
First establish you have 230 V on the line, then check the earth Warning the earth may be at 230 V!!. Stick a long screw driver in the ground and use this as your reference. There may be a voltage on the earth when disconnected possibly. The meter will see the potential difference.
If there is no voltage present, as you know the met is effectively connected to the supply, then megger between the earth conductor and the met. This will confirm the earth is non existent.
When your testing at the met the cpc's are connected to appliance's etc, eg a gas boiler which its self is connected to the water and gas, which if the services are shared with next door would also be connected to the supply, hence why your getting a reading when connected.
Regards Chris