My boss has set me a little bit of homework. A cable calculation I've found Ib,In,Iz Selected cable Ect. I now want to calculate the r1+r2 for x2 240mm2 swa cables in parallel using the swa as the CPC. I'm assuming the table in regs, giving the mV/A/m value, is not applicable when using the swa as the earth. any ideas ??
 
you need the cable manufacturers data that provides resistance values for each size of swa to calc R2.
that precise info is on this forum if you look harder ;-)
 
Thanks, I found a table values are in ohms per kilometre, so would I need to first convert these to milli ohms per meter then add the copper conductor and swa values together then this gives me the - milli ohm /m value
 
i find it easier to calculate R1 from the copper ( figures in osg ) and separately calculate the R2 from figures obtained for the armor. then add the two together.
 
I may be looking at the wrong table, but only goes to 50mm, the figure I found online was 0.0754 ohms per kilometre so would be only 0.019 ohms for my 260 meter run this seems really low even for a cable as large as 240mm, I got 0.124 over 260 meters for the r2 which seems realistic
 
resistance of swa for 240mm 4 core is 0.54 mO/mtr*
resistance of 240mm conductor is 0.075 mO/mtr*

* at 20 deg C

i've given you all you need to finish your homework ;-)
 