Has anybody got a decent knowledge of the principles on how a chiller operates alongside cooling tower and air handling units??????????
 
Has anybody got a decent knowledge of the principles on how a chiller operates alongside cooling tower and air handling units??????????

I'll assume within your system you have a chiller/s, cooling water pumps, chilled water pumps and cooling towers. The chiller will be full of refrigerant running through it, also within the chiller unit you will have the chilled water and cooling water systems pumping through it, the chilled water is generally a closed loop system. The refrigerant is used to reduce the temperature of the chilled water then off to the load (AHU or Building, whatever), the refrigerant while doing this will expand/compress/gas/liquid and heat up, the cooling water system will be pumped through the chiller to take the heat away from the refrigerant, this water is then transfered up to the cooling towers where fans blow over the water to take the excess heat away and cool back down. All of the above will all have temperature controllers fitted to control. This is a basic discription, hope it helps and there are also good web site from which this information is available.
 
Where i used to work we had cooling towers keeping the oil in the moulding machines at a reasonable temperature, and chillers keeping the mould tools cool, as chillers keep a tighter tolerance on temperature rather than cooling towers.
 