Discuss Clients requirments in the UK Electrical Forum area at ElectriciansForums.net
G
Graham Coughlan
The client has specifically requested three phase fan units to be fitted, each appliance draws a current of 8.67A from a 400v, 50hz ac supply.
One appliance is wired using 21m of multi core 90°C themo-setting insulated non shealthed cable.
The circuit is protected by a triple pole bsen 60898 mcb type c. The cable is to be incorporates into pvc rigid conduit fixed surface mounted in an area where ambient temp is 40c.
The conduit will also partlynbe used for 6 x 2.5mm2 standrd single pvc cables...
Ive gotta find...
1 the rating of the protective decive
2 the relevant correction factors
3 min cable size required
4 max size of cable
5 max permmited volt drop
6 actual volt drop
Right so far ive got
a)
10A
b) C[SUB]a[/SUB] = 0.91
c) Minumin cable size = 1.5mm[SUP]2[/SUP]
d) Maximum permitted voltage drop = 5% of 400v = 20v.
e) Vc = (Mv/A/m) x Ib x L / 1000 = 4.55v
Im not sure what other correction factors i need to consider other than the ambient temp
i would say you need to calculate the volt drop per phase , using 230V. so max. permitted per phase is 11.5v.
Reply to Clients requirments in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
4K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
4K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
4K