The client has specifically requested three phase fan units to be fitted, each appliance draws a current of 8.67A from a 400v, 50hz ac supply.
One appliance is wired using 21m of multi core 90°C themo-setting insulated non shealthed cable.
The circuit is protected by a triple pole bsen 60898 mcb type c. The cable is to be incorporates into pvc rigid conduit fixed surface mounted in an area where ambient temp is 40c.
The conduit will also partlynbe used for 6 x 2.5mm2 standrd single pvc cables...

Ive gotta find...

1 the rating of the protective decive

2 the relevant correction factors

3 min cable size required

4 max size of cable

5 max permmited volt drop

6 actual volt drop
 
Right so far ive got

a)
10A
b) C[SUB]a[/SUB] = 0.91
c) Minumin cable size = 1.5mm[SUP]2[/SUP]
d) Maximum permitted voltage drop = 5% of 400v = 20v.
e) Vc = (Mv/A/m) x Ib x L / 1000 = 4.55v

Im not sure what other correction factors i need to consider other than the ambient temp
 
i would say you need to calculate the volt drop per phase , using 230V. so max. permitted per phase is 11.5v.
 
i would say you need to calculate the volt drop per phase , using 230V. so max. permitted per phase is 11.5v.


He's right with the 400 Volt calculation-it's based on line-line voltage so you use (assuming a balanced system) per phase VD X 0.866
 
agreed. 20v line/line or 11.5v line/N. ( 11.5 x sq.rt.3 = 20 )
 

Reply to Clients requirments in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
Replies
10
Views
4K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock