Could be the length of cable run with 95 parallel cables. if a fault was to occur at the far end on one cable it may not clear the fuse within the 5 sec disconnection time due to the fault current being lower in a single 95 than in a 185 cable.

Good news then, sounds like he is flexible, the Job should go well, make sure you make him a cuppa if he visits site :clap:Update had an emailing confirming the parallel supply is acceptable and the drawings are being changed tomorrow![]()
Whats worrying is that we all had expectations that the performance of 2 beats 1, yet he convinced himself the opposite. Could this be his first design ?
BTW - just got on to the back of this thread and so glad of the outcome as i have just installed 2 X 120 as being better than 1 X240 ..... was worried for a wee while
Cant argue with the logic, but it would mean accepting an unlikely double fault scenario with the design
Whats worrying is that we all had expectations that the performance of 2 beats 1, yet he convinced himself the opposite. Could this be his first design ?
BTW - just got on to the back of this thread and so glad of the outcome as i have just installed 2 X 120 as being better than 1 X240 ..... was worried for a wee while
Thx, but its in and buried. Goes hot on Thursday.