Could be the length of cable run with 95 parallel cables. if a fault was to occur at the far end on one cable it may not clear the fuse within the 5 sec disconnection time due to the fault current being lower in a single 95 than in a 185 cable.
 
Could be the length of cable run with 95 parallel cables. if a fault was to occur at the far end on one cable it may not clear the fuse within the 5 sec disconnection time due to the fault current being lower in a single 95 than in a 185 cable.

Cant argue with the logic, but it would mean accepting an unlikely double fault scenario with the design
 
Update had an emailing confirming the parallel supply is acceptable and the drawings are being changed tomorrow :)
 
Obviously, he has eventually seen the error of his argument. A parallel supply will in most circumstances, be far superior than a one large cable. And you will only need to provide one suitably sized separately run CPC, not Two!!
 
Update had an emailing confirming the parallel supply is acceptable and the drawings are being changed tomorrow :)
Good news then, sounds like he is flexible, the Job should go well, make sure you make him a cuppa if he visits site :clap:
 
Whats worrying is that we all had expectations that the performance of 2 beats 1, yet he convinced himself the opposite. Could this be his first design ?

BTW - just got on to the back of this thread and so glad of the outcome as i have just installed 2 X 120 as being better than 1 X240 ..... was worried for a wee while
 
Whats worrying is that we all had expectations that the performance of 2 beats 1, yet he convinced himself the opposite. Could this be his first design ?

BTW - just got on to the back of this thread and so glad of the outcome as i have just installed 2 X 120 as being better than 1 X240 ..... was worried for a wee while


Plugsandsparks,
Oh dear,"what have you done"

This was one big wind up for sintra,we were all in on it
"Marvo" was in fact the consultant

Apologies for not letting you in on the joke earlier
 
Cant argue with the logic, but it would mean accepting an unlikely double fault scenario with the design


It would only need a single fault ie cable damage on one cable. This could cause the cable to burn back rather than clearing the fuses as the fault current would be too low due to loop resistance over a long run This is especially true with aluminium cored cables as they tend to burn whereas copper melts and is more likely to weld cores together giving lower resistance faults.
 
Whats worrying is that we all had expectations that the performance of 2 beats 1, yet he convinced himself the opposite. Could this be his first design ?

BTW - just got on to the back of this thread and so glad of the outcome as i have just installed 2 X 120 as being better than 1 X240 ..... was worried for a wee while


I wouldn't have used 2 X 120mm To replace a 240mm cable, that's for sure. 2 X 95mm will give you a little more CCC than the 240mm and will still stay within other determining factor criteria so long as the overall install distance is not excessive!!
 